flow velocity in low gpm zones
Last Post 15 Feb 2012 04:17 PM by acwizard. 3 Replies.
Author Messages Resolved
AMACUser is Offline
15 Feb 2012 12:01 PM
Hi All,
First post and i can't get the search function to work. Sorry if my question is addressed already.
I have read John Siegenthaler's book "modern hydronic heating". I am working out some designs for my house and have a problem with flow velocity. I have a situation where i have 6 circuits of about 200' in length each, this constitutes a zone. When resolving this setup in parallel, the flow rate required in each circuit is low (.4 gpm). This gives flow velocities of about .65 ft/s. This is far away from 2-4 ft/s recommended to keep air in suspension. I understand that the common piping will flow faster and therefore remove air where the actual separator is located, but will the individual circuits be a problem?
AMAC
15 Feb 2012 02:14 PM
no. the 2-4 ft/s recommendation is really pretty silly. in radiant loops this recommendation is routinely ignored.
AMACUser is Offline
15 Feb 2012 02:36 PM
Many thanks!
acwizardUser is Offline
High velocities are noisy, pump hp is greater, and the possibilities of piping erosion are real. 8 feet per second is the maximum velocity pex tubing should be subjected to.