Any pump that you install will circulate water at some flow rate. The real question is whether the pump that you install will supply the proper flow rate of water at your supply temp to produce the desired floor temp and associated zone heat gain.
If you have 6 circuits that are each 250 feet long being feed by a Grundfos UPS15-58FC pump at the lowest speed setting (speed 1), your flow rate in each circuit will be 0.73 GPM (or 4.36 GPM total) at 5.76 feet total head.
At the Grundfos UPS15-58FC pump middle speed setting (speed 2) your flow rate in each circuit will be 0.99 GPM (or 5.92 GPM total) at 9.83 feet total head.
At the Grundfos UPS15-58FC pump highest speed setting (speed 3) your flow rate in each circuit will be 1.13 GPM (or 6.78 GPM total) at 12.45 feet total head.
If you have 8 circuits that are each 250 feet long being feed by a Grundfos UPS15-58FC pump at the lowest speed setting (speed 1), your flow rate in each circuit will be 0.64 GPM (or 5.13 GPM total) at 4.69 feet total head.
At the Grundfos UPS15-58FC pump middle speed setting (speed 2) your flow rate in each circuit will be 0.89 GPM (or 7.10 GPM total) at 8.29 feet total head.
At the Grundfos UPS15-58FC pump highest speed setting (speed 3) your flow rate in each circuit will be 1.03 GPM (or 8.25 GPM total) at 10.79 feet total head.
BTW, PexSupply.com is one of our affiliates and a great place to buy hydronic radiant floor heating system components. We also prefer Grundfos pumps over Taco pumps too.
Happy Thanksgiving