As a follow-up I've moved forward in some areas and took some advice from your above posts- thank you.
1. Had the closed cell foam installed and the "great room" is able to maintain 65' inside temp (without any baseboard in the room or radiant) while outside is low 41's. 3" +/- ceiling and 2" +/- walls.
2. Looked into LoopCAD in depth and updated my floor plan with windows, doors and proper insulation values. I also added the actual design layout of my radiant tubes.
3. Purchased "Omega" shaped radiant heat plates from an eBay vendor. They are thin, but the cost difference was huge (Uponor $1.8k vs. $400). I plan to install them next weekend - probably with a puematic staple gun. My plan is to run R-19 Fiberglass bat's under the plates in the joist bays.
4. Changed my control strategy after speaking with an Uponor engineer. They strongly recommended moving away from the constant circulation system and using Taco Zone controls, thermostats with slab sensors and zone control actuators. The pricing isn't bad and this is what I was thinking to begin with.
Before all the below images take up the rest of this post I have two questions:
1. Basement heating issues: My basement seems to require 9k BTU/hr and I am trying to maintain a low water temp throughout the house. Choices:
1.A. Synergy Baseboards offer ~320 BTU's per foot at 4 GPM & 120' water, but the one price source I found seemed to indicate they were very expensive and I will need 27' of baseboard...
1.B. Install PEX tubing and create a radiant wall on the lower 4' of the room. LoopCAD doesn't have an option for this so I don't know how much Pex is required or the BTU/HR output.
1.C. Find some type of hidden cash and have the basement slab broken up, foam installed, pex tube, concrete pour. (I don't have the funds I think).
1.D. Alternative heating solutions? I'm open to anything.
1.E. I plan to follow the above advice for the garage and basement with foam boards and fiberglass so I will seal this space up as best as possible. It is also half below grade so it has that going for it and I'm not sure what my downward losses will be on the now staple-up/thin transfer plate Pex & R19 below it.
2. Pump sizing and recommendations? I tried to follow Taco's document "TD10" and calculated I need a pump that flows 1.3 gpm for my radiant system. LoopCAD tells me the total flow of the manifold is 2.34 gpm. I'm a little confused here.
3. By changing from constant circulation to zones and floor sensors will I have a lot of noise from the heat transfer plates? If so anything I should do to prevent this?
NOTE: After reading TD10 I now know I should be using 5/8" PEX due to min/max flow ratings of the tube. I think 3/4's minimum flow is 2.3 gpm which would be all circuits running.