Geothermal well cost
Last Post 28 May 2009 09:23 AM by Bergy. 47 Replies.
Page 3 of 3 << < 123
28 Feb 2009 08:56 PM
bman...
If your target loop temp is 30°,  the 50° temps found below 30'  can give you a lot more heat per foot of pipe than the 40° temps  found at 5' deep.
Mary,  you are right, the chart is for northern  US climates.  Soil type and moisture content all play a part in loop design,  with moisture having the most effect.
waterpirateUser is Offline
01 Mar 2009 03:27 PM
The cost of drilling here on the Delmarva Penninsula is now free!!!!
The average cost of the drilling for any given residential project is 20-30%. That coincides with the stimulus package and I am projecting an extremely busy 2nd quarter. WHOOHOO!!!
25 May 2009 12:16 PM
Using the Geolink software, I don't see much difference in vertical vs horizontal loop lengths.  The grout on the vertical has a similar effect as additional tubes or slinkys (contact with more soil).  But you could grout a horizontal loop too.
I've seen references to ground water flow being a factor in vertical loops.  This would argue that it is best to maximize the amount of vertical loop that is in sand or gravel (ie, 2x200'  holes might outperform one 400' hole if you have sand from 100' to 200').
Except for these two issues, I would expect no difference between a 30' horizontal loop and a vertical loop.
26 May 2009 09:25 AM
Posted By jonr on 05/25/2009 12:16 PM
If soil and weather were constant and predictable, you might be right, but as they are not, a horizontal loop must be built for extremes that a vertical loop will not be affected by. Soil issues close to the surface may not affect vertical wells, so our horizontals may run as much as 600' longer than verts, I don't think you can credit the grout with 3 times the soil contact (remember there are 2 pipes per bore). -18* in MI causes long operating cycles that affect both types of system, but it also affects shallow ground temps with little impact on verticals I don't think you'd find grouting would get it done on a short horizontal.
The difference between paper engineering and contracting is provision for the uncommon. Most formulae don't include that.
I say this because you seem to be trying to "nut-shell" ground loops which can be done to some degree, but you have to remember all of the components of the equation. Loop designers will often have a X'/ton rule that they use. This results in oversized loops in many situations, but why throw away 50' of pipe/ton if you have a 600' roll and only 550' is indicated?
Good Luck,
J
27 May 2009 07:07 PM
The main function of the grout in a mud rotary borehole is to seal the hole, not enhance conductivity. The main function of the grout in a air rotary hole is to provide a thermal link in a dry hole, plus seal the hole. You are corect that a saturated loop will provide better conductivity than say a shale hole, but to compare the vertical with the horizontal is comparing apples and bannanas.
The two types of exchangers pose very different issues that are addressed in the design phase of a project. If all things are equal a design for a horizontal system and a vertical system, in regard to loop lenght for the same piece of dirt will never yield the same ewt and lwt.
roooooomieUser is Offline
28 May 2009 06:22 AM
How can you "oversize" a H loop? The cost for moving the extra dirt and piping is nil compared to the insurance you get for more extreme weather condiions... not "overizing" the horizontal is short changing the customer.
28 May 2009 08:57 AM
Posted By roooooomie on 05/28/2009 6:22 AM
Right sized is not undersized. (right is not wrong). This notion that 50' might have a real impact on operating temperature is silly. As is the notion of insurance loopage. A 5 degree change in loop operating temperature could easily be twice the pipe (depending on soil and moisture present). I've commented before that certain target loop operating temperatures are not the Holy Grail of geo (perhaps you missed my tirade on that one).
Loops that are "close enough" to size will treat you much better than undersized ductwork, improperly sized heat pumps or a contractor that doesn't set the unit up correctly.
You speak from ignorance when you suggest (by the quotation marks around "oversizing") that I (or any other contractor) am short changing my customers. A properly designed system is just that.....properly designed.
How about oversizing equipment while we're at it, instead of shooting for 95% of the load, I should go for 100% so that after spending several thousand bucks on duct work equipment and ground loops your operating cost should be $50/year less since we won't run (the anti-christ) that evil auxiliary coil.
Tirade concluded:)
Roomie,
Remember that loop size is just part of the equation.
When I suggest that dropping 50' extra feet in the ground is "over-sizing" that is because it is on top of what was required for my design load. My loop design can be 20, 30 or even 40* depending on what a customer wishes to pay for.
Not short changing, just business. If you want to pay for extra, you can. If you want something for nothing, can't help ya.
Good luck,
Joe
BergyUser is Offline
How can you "oversize" a H loop? The cost for moving the extra dirt and piping is nil compared to the insurance you get for more extreme weather condiions... not "overizing" the horizontal is short changing the customer.[/quote]
Roooooomie,
As loop lengths increase, so do pumping costs. There is a point of diminishing return where the "slight" increase in efficiency is off set by the pumping costs. The only time we the customer gets "short changed" is when the loop is not properly designed.
Bergy
People Online People Online: Visitors Visitors: 187 Members Members: 0 Total Total: 187