Getting back to the original question are the headers and loop pipe sizes the source of any mal-performance of the system?
When designing the header system the primary concern is the pressure drop for each header segment. In the parallel flow arrangement, the first supply header pipe carries the total volume for all loops. As each loop is supplied, the flow rate to the next supply segment is reduced by one loops worth of flow. A well designed header system should have roughly 4' of head loss per 100' of pipe length. In larger systems, this is very important to reduce pumping power costs. However, for a small 3 borehole system, using 1 1/4" inch pipe for the main header is not a huge problem. The impact is a small increase in pumping power.
More important to the system operation is the actual flow rate being achieved through each loop. As long as the flow is within the turbulent flow regime, there should be good heat transfer between the circulating fluid and the pipe wall. Also important to the heat transfer is the proper grouting outside the pipe. If the loops were not grouted properly there could be air spaces between the pipe and the soil. The air spaces dramatically impede the system performance.
Although not normally addressed in residential systems, the thermal conductivity of the soil has a significant impact on the system performance. Soil conductivity can triple the amount of loop length required to meet a given system load. It is possible that this installation is in low conductivity soil. Due to the high cost for a thermal conductivity test (~$4000-$5000), it is often wise to simply investment in more holes. However, if there is a concern with the performance of an existing system, it is possible to determine the ground thermal conductivity by measuring the flow rate, supply temperature, and return temperature over an extended period of time. Thermal modeling software can then be tuned to match the system performance and thus determine what ground thermal conductivity would yield the same performance.
It is important to perform basic troubleshooting on the system prior to examining the detailed performance but it is possible to model virtually any system design to determine the impact of improper design or installation.
I hope this adds to the discussion,
Jim Bererton, P. Eng.
Manna Solutions Ltd.
[email protected]