Posted By tuffluckdriller on 02/07/2008 12:09 AM Those heating loads seem awful high to me for that size of house. What are the parameters they are using? Have they padded the numbers a lot as a safety on their load calculations, did they? What programs are they using, and can they really back up those numbers? What is the winter design temperature?
I'm in Utah, in the coldest part of the state (for this year). On a new 1800 sq. ft. home, I can't imagine the loads are really that high. You need to really scrutinize what they are telling you.
I'd really suggest you look in to a DX geothermal heat pump. EarthLinked is a good one.
Good luck. The 4 ton and 3 ton bids are using the same design temperatures of -4 and 93 degrees. Also the average internal gains are very different. 3 ton is 7793 and 4 ton is 12692. As far as the pumps, everyone in the area sells WaterFurnace, GeoComfort, or Climate Master. We are going to talk to three of the four bidders and ask that they explain why eveything is so different as far as numbers. |
|
|
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 08 Feb 2008 08:39 AM |
|
Posted By IowaGeoHope on 02/07/2008 6:05 PM
As far as the pumps, everyone in the area sells WaterFurnace, GeoComfort, or Climate Master.
Just Curious, are these the only major vendors for Geothermal systems? Does anyone have a complete list of manufactors? |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 08 Feb 2008 08:49 AM |
|
Posted By TechGromit on 02/08/2008 8:39 AM
Just Curious, are these the only major vendors for Geothermal systems? Does anyone have a complete list of manufactors? See this postMcQuay is not on the list so I know it is not complete What brand is yours?
|
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
IowaGeoHope
 New Member
 Posts:15
 |
| 08 Feb 2008 06:16 PM |
|
Hey geodean. We downloaded the software you pointed us to, took the 10 minute video, and are now plugging in the numbers. They certainly ask a lot more questions than the HVAC contractors did. This program is like the Res Check we did (we are our own General Contractor) so we were pretty comfortable with all the information they were asking. We will post and let everyone know what we came up with as far as loads. This should be interesting.
|
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 08 Feb 2008 07:01 PM |
|
thanks for the update, anxious to hear the outcome |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
IowaGeoHope
 New Member
 Posts:15
 |
| 08 Feb 2008 07:02 PM |
|
Okay, we have run the numbers and have a question. The basement: 1800 sq ft, one daylight window and two standard 5.7 sq ft egress windows. There will be an R10 blanket on the walls. Living in Iowa the basement will have a few heat registers to keep the basement "warmer" in the winter months. In anyone's opinion would you consider the basement unheated or a conditioned space? The heat numbers go from 57,000 for unheated to 32,000 for conditioned. |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 08 Feb 2008 07:14 PM |
|
In Utah, we always heat the basements. Remember that if unheated then the mainfloor is over unconditioned space which requires more heat. Did you select the below grade option for the basement walls? And there is nothing entered for the ceiling value in the basement since the mainfloor is heated. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 08 Feb 2008 10:58 PM |
|
Posted By geodean on 02/08/2008 8:49 AM
Posted By TechGromit on 02/08/2008 8:39 AM Just Curious, are these the only major vendors for Geothermal systems? Does anyone have a complete list of manufactors?[/quote] See this postMcQuay is not on the list so I know it is not complete What brand is yours? I have a "Florida Heat Pump" FHP Manufacturing Division Model LTV-50-1 230/208v Compressor 230/208 Volt, 17.6 RLA, 88 LRA Blower 230/208 Volt, 1/2 HP, 4.1 FLA Anyone know what any this means? I wouldn't mind getting a manual for it. |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 09 Feb 2008 10:27 AM |
|
Posted By TechGromit on 02/08/2008 10:58 PM Anyone know what any this means? I wouldn't mind getting a manual for it.
Here is a list of all the models that Florida Heat Pumps makes. I don't see yours on there. You can inquire about yours here . When I asked about mine, I did get a reply. Did you ever confirm if yours has back up heat? My guess is that it does. If there is a junction box inside the upper cover, you could look in there to see if there are leads going into the air box. Back up heat is located at the very top of the unit right below where the duct work hooks on. Good luck and let us know.
|
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 09 Feb 2008 10:29 AM |
|
Posted By IowaGeoHope on 02/08/2008 7:02 PM The heat numbers go from 57,000 for unheated to 32,000 for conditioned.[/quote]
I just can't believe that your house needs 57,000 btuh. If you will send me all of the input data, I would like to run the numbers on this myself. My house is 1700 sq ft with a basment and my heat loss is 43000 btuh. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
tuffluckdriller
 Advanced Member
 Posts:630

 |
| 10 Feb 2008 11:55 AM |
|
TechGromit,
It's a 230 Volt compressor, with a run load amps (amps that it uses while running) of 17.6A, and a Locked rotor amps of 88. FLA is full load amps, or when the motor is under full load, it's drawing 4.1 amps.
|
|
| Clark Timothy ([email protected])<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com |
|
|
tuffluckdriller
 Advanced Member
 Posts:630

 |
| 10 Feb 2008 11:56 AM |
|
Iowa Geohope, did you get my message? |
|
| Clark Timothy ([email protected])<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com |
|
|
IowaGeoHope
 New Member
 Posts:15
 |
| 10 Feb 2008 05:08 PM |
|
TuffLuckDriller - We did receive your mesage and sent a response by private message on 2/8 and again on 2/10. Thank you. |
|
|
|
|
IowaGeoHope
 New Member
 Posts:15
 |
| 10 Feb 2008 05:11 PM |
|
Thank you to everyone for all the help. We have both run our own numbers and GeoDean ran numbers, all using the same program. Roughly, we all landed at 32,000 btuh heat loss. Factoring in the 20% safety margin recommended by the program we all end up at 38,400 btuh. As professional heat contractors, or any one who else who wants to weigh in on our question, would you look me in the eye and say “Go 4 ton as 3 ton is really marginal.” Iowa winters are harsh and we do end up with several below zero days a year. The last two days here have been rough with 40 mph winds and a temperature that did not get above 4 degrees. Please, all we want is an honest answer. 3 ton or 4 ton? If it were you, what would you do? |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 10 Feb 2008 05:23 PM |
|
I would go with the 4 ton. My house is about the same size as yours, not quite as well insulated and I have a 4.5 ton. I didn't design my system, but I monitor very closely how it works. It keeps my house plenty warm in the winter. Cooling works well also.
There is nothing wrong with buying yourselves some peace of mind.
I would recommend a two stage heat pump, then when cooling, you can have longer run times on first stage to get better dehumidification. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
IowaGeoHope
 New Member
 Posts:15
 |
| 10 Feb 2008 06:21 PM |
|
Thank you for the answer. We have been vacillating over this question for several weeks. All the systems we have had bid are three stage heating and two stage cooling. After your numbers and our numbers we realized a 3 ton wasn’t going to work. Geo is the thing we are absolutely going to do. Based on all the information you have all so kindly posted, we will be talking to several HVAC contractors and challenging their heat loss numbers. |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 10 Feb 2008 06:40 PM |
|
Good Luck and keep us posted. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
tuffluckdriller
 Advanced Member
 Posts:630

 |
| 10 Feb 2008 09:40 PM |
|
Yep. With the numbers, I'd stick with a 4 ton. |
|
| Clark Timothy ([email protected])<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com |
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 12 Feb 2008 03:49 PM |
|
Posted By geodean on 02/09/2008 10:27 AM
Quote, FHP does not make "owners manuals" or "operation & maintenance" manuals. The only thing available would be wiring schematics but we only send them to licensed Contractors. Regards, Greg Dunn Technical Support Well they were really helpful, NOT! That's something that really Urks me about some companies, no support. I have an electric Corona chainsaw on a pole and I go to the website for support and there zero information about it. They answered one question someone asked about it, but that's it. What would it cost them to put a PDF manual online for it? About 2 cents? So they don't sell or make it anymore, so what, they should throw some documention online about the product under discontinued products so when I need to buy a replacement chain for it, I dont have to guess what size I need. A geothermal system isn't a 99 dollar chainsaw, if I'm spending 20k on a geothermal system I want a friggin manual for it! Is that too much to ask? When I have to replace my system, one of the things I'll be looking at is what kind of online support they offer for what they sell / have sold. WaterFurnace has an impressive amount of info for there products online, I don't even own one and i see a spec catalog that lists picture of components, features, tables and wiring diagrams. What's the big secret with wiring schematics anyway, it's not like I'm going to rewire the system just for fun. |
|
|
|
|
tuffluckdriller
 Advanced Member
 Posts:630

 |
| 13 Feb 2008 07:14 PM |
|
FHP is just a lower end unit, compared to WaterFurnace. That's not to say one is better than the other, but price-wise, they are worlds apart. |
|
| Clark Timothy ([email protected])<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com |
|
|