TechGromit
Advanced Member
Posts:634
18 Feb 2008 03:56 PM
I've been told that insulating my basement would save between 20k to 27k BTU of heat loss. My initial response was doubtful, since the basement isn't heated anyway. When I thought about it, since the basement is cooler than the 1st floor above it, it would tend to cool off the first floor faster then it should. I know that 20k BTU is just a rough estimate, but is there a formula I could apply to figure out what my actual BTU heat loss currently is. I would think that a 10 x 20 foot uninsulated basement would have the same heat loss per sq foot as a 20 x 50 uninsulated basement. And number two, how much can I expect to save per 1k BTU heat loss if I insulated the basement. This would give me a cost / benifit ratio I can use to justify the expense of insulating.
Palace Geothermal
Veteran Member
Posts:1609
18 Feb 2008 04:35 PM
Attached are two heat loss calculations from a house. The first has no insulation in the floor. The second has R 30 in the floor.
As you can see the difference is about 20k BTUh.
This is for total floor footage of 2700sqft.
1 kw is about 3400 BTU. If your heat pump has a COP of 3 then you get about 10k BTUh for each kw you buy. So based on your kw rate, you can figure your savings.
Hope this helps.
Attachment: no floor insulation.pdf
Attachment: with floor insulation.pdf
Dewayne Dean
<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
TechGromit
Advanced Member
Posts:634
18 Feb 2008 07:23 PM
Thanks for the PDF files! Over what period of time are these figures for? Daily Averages?
Thanks!
Palace Geothermal
Veteran Member
Posts:1609
18 Feb 2008 07:26 PM
These are BTU's per hour at the design conditions listed at the top of each report.
This particluar house was designed for an outside temp of -10° F. So when it is -10 the heat loss will be what is listed on the report.
Dewayne Dean
<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
You are not authorized to post a reply.
Green Building Forums
--General Forum - Residential
--General Forum - Commercial
--Green/Energy-Efficient Design and Planning
--Green/Energy-Efficient Building and Construction
Green Building Technologies
--Insulating Concrete Forms (ICFs)
--Structural Insulated Panels (SIPs)
--Radiant Heating
--Geothermal Heat Pumps
--Solar and Wind Power
--Windows/Doors and Interior/Exterior Finish
--Appliances, Lighting and Kitchen/Bath Fixtures
Feedback/Support
--Rules, Instructions and Announcements
--Suggestions/Feedback
--Testing Area
Forums
>
Green Building Technologies
>
Geothermal Heat Pumps
Active Forums 4.1
Membership:
Latest:
croccohvacusa
New Today:
0
New Yesterday:
1
Overall:
35027
People Online:
Visitors:
201
Members:
0
Total:
201