Posted By SkiHawk on 07/24/2008 11:59 AM
1) Currently I have an unheated basement, which I don't plan to heat in the future. Does this need to be in the overall calc? I'm thinking not.
No. But you should treat the floor as 'Above Unheated Space'.
2) I also have a whole-house fan that I try to seal very well in the winters. Do I need to include this as some kind of window?
I wouldn't.
3) I have two fireplaces in my house. One that I don't use, so I have seal with an outside and inside damper, plus some plastic inside. I also have 42" wide fireplace that I do use in the winter. In the HVAC Calculator I put "Average" and it adds about 7000BTU to the loss, if I do 'Poor' I loose about 14000 BTU. This fireplace does have a damper. Do I really need to put it as 'Poor'. It seems to really raise my loss.
That is toally your call.
So when I add everything up (the way I have it configured now) I get 42,000 BTU as my loss. (No Basement, "Average" Fireplace). My house is 2100 sq ft of heated living space.
That sounds a bit low. Where do you live? Also, be careful with wall R-Values. They s/b treated as 'Whole Wall' and not just the value of the insulation. A stud is about an R-6 for a 2x6 wall. And they are every 16"
Good Luck!