Methanol or Propylene Glycol
Last Post 23 Aug 2008 12:04 AM by joe.ami. 8 Replies.
SmileyBurnetteUser is Offline
19 Aug 2008 10:53 AM
How do I tell if my ground loop has Methanol or Proplylene Glycol as the antifreeze?  Which is better?  Is it OK to mix them?
19 Aug 2008 11:14 AM
Not sure how you can determine which you have.  Any chance of asking the installer?
You can not mix them!!!!
 Methanol water has a low frictional pressure drop and a relatively high heat transfer coefficient. However, it is highly volatile, highly flammable, and highly toxic until diluted.  Low cost.
Propylene glycol solution is an alternative with the only true advantage of being less toxic than  methanol. Below about a 20°F freezing point, the viscosity gets excessively high, resulting in high pumping costs.  High cost.
19 Aug 2008 11:20 AM
You could tell by checking the specific gravity of the solution. Methanol will be less than 1.0, Glycol will be more than 1.0.
19 Aug 2008 11:24 AM
Thanks for the quick response!
The geothermal was installed 15 years ago when the house was built.  I just bought the house.  I don't know who the installer was nor did the previous owner.
I guess I'll have to figure out how to do a specific gravity test.
19 Aug 2008 01:14 PM
are you worried about the level of freeze protection?
20 Aug 2008 09:40 AM
Yes, freeze protection is the issue.  To accomodate some remodelling, the interior piping was moved.  This resulted in some fluid loss that we replaced with straight water.
20 Aug 2008 09:46 AM
Methanol has a pretty strong smell, while glycol is odorless.
21 Aug 2008 02:58 AM
Low tech test - Methanol should have a distinct alcoholic smell whereas a couple drops of the glycol should feel quite slimy between two fingers, like soap.
Just a thought.
If "some fluid loss" isn't much, water replacement probably OK. If the loss ran to several gallons, then freeze protection likely compromised
Where are you located?