Don't Wait
Last Post 03 Oct 2008 09:14 AM by senecarr. 92 Replies.
Page 2 of 5 << < 12345 > >>
vhehnUser is Offline
18 Sep 2008 01:27 PM
i see these huge numbers for instalation costs and wonder if people and thinking emotionally instead of rationally.
for most climates a good air source heat pump will be most cost effective.
conniepanganUser is Offline
18 Sep 2008 02:09 PM
I researched that air source heat pump doesn't work in the extreme cold climate like Northeast. I would definitely go towards this if it's feasible.
senecarrUser is Offline
18 Sep 2008 02:36 PM
Actually for many climates it won't work. You still need a back-up heat source like propane (if that's what you're on as many looking this route are). The kicker then is, you're now buying less units of propane, so the company gives you a higher rate. Most of the installers on this sight are probably the nightmares of Hank Hill, and they sure don't want you getting off their product. There's also a question of durability. I've generally seen the loop fields getting a 25 or 50 year warranty on parts, which means the hardest part to install on a geothermal lasts a long time. I can't imagine many heat pumps are going to stand behind their devices operating down to -30F every winter for many years.
183eejUser is Offline
18 Sep 2008 03:54 PM
Posted By Bruce Frey on 09/18/2008 11:38 AM
For fun, I ran the following net present value calculation:
20 years (240 months)
$1200/yr ($100/month) current savings excalated at 10%/year for utility cost increases
3% annual inflation rate
The NPV is ±$47-52k depending on whether you compund monthly or annually.
The greater the spread between utility inflation and annual inflation, the larger the number.
At 15 years, it drops to ±$28k and to ±$15k at 10 years.
It definitely justifies the expenditure and should justify a higher valuation or sales price.
Bruce
This is intriguing.  But I haven't been able to replicate your calculation in Excel yet.  Did you do this in Excel?  If so, I was hoping you might be able to post a copy I could look at.
Dale Walker<br>EarthTap<br>www.earthtapenergy.com<br>Where the sun never sets on energy savings<br>
18 Sep 2008 11:25 PM
Regarding value added or subtracted to homes too much is in the eye of the beholder for software caculation, which is why we're looking at realestate comps. not predictions. As many are oblivious to geo, we started with the detractor of propane or oil which most do seem to understand.
RE airsource heat pumps, Seneca and I ran cost projections for his home and found that the return on investment was about the same (assuming propane prices stayed flat.....). Of course if you could save a thousand a year on a 4K investment or 5K a year on a twenty thou investment and both continued their return after the first 4 years, which would you choose?
J
19 Sep 2008 07:53 AM
Posted By joe.ami on 09/18/2008 11:25 PM
J
I agree that there is an art component to pricing homes.
However, there is also a pattern.  And patterns have a predictable nature that can be formulated and, done well, can get within a + or - range accuracy that can add a useful chapter to the geothermal value story.  Getting over the "first cost" hurdle is a head scratcher for a long list of people that need to include a geothermal solution in their home's heating and cooling evaluation.  With the alarming increase in the cost of utilities required to heat and cool homes that we have seen lately, I suspect energy costs may make it's way to the front of the herd as a price driver for homes.
At some point, I would expect this price driver to show up in real estate comps.  That just takes time to filter it's way through the system in an economic climate like this one where people are afraid to buy much of anything.
I see value in return on investment and net present value methods in providing tangible evidence that geothermal is a good economic decision.  Adding the comfort and safety features makes the case even more compelling.  The challenge is telling the story in a way people understand the real value they get with a geothermal investment.
Bruce FreyUser is Offline
19 Sep 2008 05:46 PM
Yes, I used Excel.  I am not sure how to post a file, but I will try to walk you through it.
In 3 separate cells insert:
Estimated Annual Inflation Rate
Annual Estimated Energy Savings
Estimated Annual Energy Inflation Rate
Create a table with 1 to X years (x = how many years you want to study) with the  the annual energy savings in the year 1 cell
In the year 2 cell, multiply the year 1 savings by 1+Annual Energy Inflation Rate.  If year 1 savings is 1200 and annual energy inflation rate is 10%, the year 2 value will be 1320.  Copy the cell into years 3 to X.
In another cell, use the NPV function.  It will be =NPV(Annual Inflation Rate,range of cell of years 1 to X energy savings)
IF:
Annual inflation = 3%
Annual savings = 1200
Annual energy inflation = 10%
for a 20 year table year 1 = 1200, 2 = 1320, etc to 20 = 7339
NPV = 46712
You can also include your initial investment as a negative number in year 0.  In the above example, if the initial investment is -20000 the NPV is 25943.
The math is easy.  The hard part is correctly estimating the numbers.  This is good tool for comparing different scenarios and sensitivities.  As someone said, the value is somewhat in the eye of the beholder.  You cannot put NPV in the bank, but it does demonstrate in a relative way how much value is created.
Send me a PM with your email address and I will send you a file if you wish.
Bruce
19 Sep 2008 06:07 PM
To post a file, you need to hit the reply above someone and then it will show you the full reply instead of the quick reply. The file should look something like the attached. Yesterday I thought I had the math wrong, but I realized today you weren't subtracting the initial investment from your figure, but I was. To use the file, rename the type (last 3 letters after .) from pdf to xls. Forum doesn't want me posting xls files, probably to avoid macro viruses.
Attachment: geoNPV.pdf
19 Sep 2008 07:26 PM
Posted By Bruce Frey on 09/19/2008 5:46 PM
IF:
NPV = 46712
Bruce
Thanks Bruce.  Regarding the 3% inflation assumption, if you borrow the money to buy geothermal with a fixed rate mortgage, wouldn't the inflation be zero since the monthy payment amount is fixed?  The other thing I am thinking about is the tax deduction for the interest on the mortgage and how it impacts the NPV.  Any thoughts?
19 Sep 2008 07:43 PM
Posted By senecarr on 09/19/2008 6:07 PM
Thanks for the tip.  I was trying to save an Excel file this morning and wasn't understanding why it wouldn't work.
The NPV approach can tell a powerful story for geothermal.  This is great stuff.
20 Sep 2008 02:56 AM
Changing the file type generally corrupts the file (as I think happened here).  The forum does not support posting Excel files and I figured that printing it as a pdf would not be helpful because it does not show the spreadsheed construction, just the answer.
Bruce
20 Sep 2008 03:29 AM
My previous repy was a bit incomplete due to lack of coffee this morning.  That is a good trick.  My experience with changing file types is that it corrupts the file.  I have changed the file type to pdf, but the forum will still not let me upload, so I am not doing something correctly.  I am trying it again by saving the excel file as a pdf.............still no luck.
Net Present Value is used to determing the present value of a series of positive or negative cashflows based on an interst rate.
I do not think the using NPV function to reduce each year's saving and then totalling them is quite correct.  If you do a 50 year study, you should also plan on replacing the compressor once or twice.  I would calculate the NPV in you 50 year study as 398935.
Bruce
20 Sep 2008 03:55 AM
Posted By 183eej on 09/19/2008 7:26 PM
This is the difficult part.....the assumptions.  Inflation (or an interest rate) is a real part of these calculations.  Another rate that could be justifiably used is the rate of return you could get for an alternate "investment."  Again, NPV  is better used as an comparative tool than an absolute one.
If you take out a loan, you should have fixed payments.  These payments would offset your energy savings, but would eliminate or reduce the inital pament.  For me the correct methodology would be to use your net annual payment/savings (which could include tax benefits).
You can go crazy if you make it too complex and try to figure depreciation, tax implications, etc.   I am not a numbers guy. I know enough about this to be considered dangerous by my number crunching MBA colleagues.
Remember the old saying "figures don't lie, but liars figure."  A good example is Wall St. today.
Bruce
BrockUser is Offline
20 Sep 2008 04:10 PM
If you want to email me the excel file I can post it on my site and link it here for anyone to grab. Just email to me at
nevermab at uwgb.edu
21 Sep 2008 09:36 AM
nonsense. i live in south dakota. it doesnt get much colder than that.
there is no need for propane backup. the electric strips will do fine.
sure they will kick on often at 0 or less but it doesnt stay that cold very long.
my hvac bills average about 50 per month. how long will it take to roe an 80k
geo investment saving half of 50 per month?
21 Sep 2008 09:52 AM
Posted By vhehn on 09/21/2008 9:36 AM
If you are paying $50 a month in South Dakota and you are not using geothermal, I may need to buy a coat and move north.  In Texas, I'm paying $50 a month for everything besides geothermal.
Having said that, I'm not understanding your numbers.  At $7K per ton, an $80K system is somewhere in the neighborhood of a 12 ton system.  $50 a month to run a conventional system that big doesn't sound right, even it is a geothermal unit.
Back before he passed away, Wilt Chamberlin said he had slept with 20,000 women in his life.  A local sportswriter, Blacky Sherrod, wrote that Wilt must have gotten his addition mixed up with his multiplication.  Your numbers sounds like you have made a similar math error.  Either that or you have an extension cord run over to the neighbor's house.
21 Sep 2008 10:19 AM
Here is the link to the NPV calculation excel spreadsheet. Bruce I hope you don't mind but I threw in a total column so you can see when the system pay's itself off.
NPV Calculation
21 Sep 2008 12:00 PM
Regarding savings or ROInvestment, you guys have already glazed my eyes over. A simple, digestable, operating cost projection with side by side comparisons of different equipment routinely shows a 5 or less year pay back around here. Get your best interest rate if you have to borrow the money, but how about having an end in sight vs ever higher gas/oil bills. Pretty easy to wrap your head around. Throw in a supported 10ish percent value added to home (based on real estate comparisons of similar homes with NG or oil or propane, sold recently in the immediate area) and now we're easy to digest, supported and defensible. The only numbers that matter are the easiest to understand- how much to run; $XXX/mo- will my house be worth more; based on sales, this year in your area homes that have LP or oil sold for X% less. Our retrofit market, has a different clientelle than the techy enthusist of ten years ago. Too much information overwelms in some cases and at the very least is dis-interesting. Keep it simple, but be prepared for the more detailed questions.
Regarding the ASHP question, I'm not sure if someone has stumbuled on to the "geothermal heat-pump" site by accident or if we have been targeted for conversion :-) I honestly believe that everything has it's place, and have used ASHPs in some applications and fossil fuel appliances in others as well as electric baseboards. To suggest that one system is the catch all do all is folly. In the retrofit market of an exceptionally large home such as Seneca's an ASHP would generally be backed up by a fossil system due to the 84MBH load as opposed to a 150 amp 30K coil since as we know at some temperature ASHP's do shut off completely while GSHP's can continue to 'supplement' heat production. Lower air temperatures cut btu out puts on air source systems that generally cause us to oversize them in our area, so when in larger homes with single duct systems multiple systems would have to be used making the installation costs much higher for all electric and some fossil back-up systems. No thanks, we'll use the 6 ton package system there. We did include a split system Daikin ASHP as one of the solutions suggest for the unducted breezeway and bonus areas. Here there is electric base board available for back up once we get to 20 or so degrees out side. I'm not sold on the down to Zero system as a good ROI. And while their VRV technology looks interesting, the cost/vs benefit still has to work for my customer.
While you've picked a tough crowd for your ASHP pitch, I think you would find interest if you were to start your own thread and support those remarkably low operating costs with data.
Joe
21 Sep 2008 12:50 PM
Posted By Brock on 09/21/2008 10:19 AM
NPV Calculation
I'm with Joe....
My background is construction not accounting.   How would I use this in a sales presentation as I'm sure most consumers don't have a clue what NPV means to them when considering  a heat pump purchase.
How does NPV compare to ROI?   Which would be better to use in a sales presentation?
In the spreadsheet,  the total of the annual savings is $68,730.  This seems more impressive to me than a NPV of $25,934.
Just wanting to learn something here  please don't mock my ignorance.
21 Sep 2008 02:30 PM
Posted By geodean on 09/21/2008 12:50 PM
NPV Calculation[/quote]
I'm with Joe....
My background is construction not accounting.   How would I use this in a sales presentation as I'm sure most consumers don't have a clue what NPV means to them when considering  a heat pump purchase.  I know a lot of CPAs that don't have a clue either so don't feel bad man.  Accordingly, I don't think you can use the term NPV with a customer no matter what their background.  People are naturally suspicious of number manipulation (i.e. figures don't lie but liars are always figuring).  However, NPV is a valid way of looking at something with a relatively high fixed cost like geothermal.  So, you have to go through NPV to get to the story that people will understand.
Here's one thought my partners and I have been bouncing around here in the Dallas area.  Let's say, for example, you have a young couple interested in buying geothermal or an air sourced heat pump.  They also have two kids just out of diapers and they hope they can put some money aside for college over the next 20 years.  Because geothermal is cash flow positive in the very first month, NPV is saying they could take the money they would have sent to the electric company to run the air sourced system over the next 20 years and invest some of the savings in a geothermal system today with a fixed rate loan and the put the difference towards that college fund for their children and, in 20 years, it would be worth the $25K or whatever that amount is.
By borrowing the additional money for a geothermal system at a fixed rate, you essentially lock-in or hedge your family budget against the bulk of the annual energy inflation we will probably see over the next 20 years.  And you are able to do that with geothermal because it is so tight fisted with your family's operating dollar from the installation date going foreward.  A 10% increase on a $40 a month elecric bill for geothermal will deny me a hamburger once a month.  That difference, which gets bigger every year as energy costs increases, is what will help out that young couple with the college fund.
Another example we are pondering is a 50 year old couple planning for a fixed income retirement in 20 years and asking what they planned on doing do with the extra money they will accumulate from buying their geothermal system.
How does NPV compare to ROI?   Which would be better to use in a sales presentation?  NPV is the accumulated dollars of an investment.  The ROI is the rate at which those dollars accumulate.  One way of looking at ROI is to compare the return on investment to the historical investment returns of the stock market.  Most people agree that, over time, the stock market will return about 10% a year so, if an investment in geothermal exceeds 10%, it's a smart money investment.
Of course, when you talk about return on your money, it's important to keep in mind Will Rogers' wise crack to Wall Street when he said he was more concerned about the return of his money than he was the return on his money.  People have to believe geothermal will deliver the baby.  If they don't, it's all labor pains for the sales guy.
All of this, I believe, is predicated on a rock solid ACCA Manual J calculation coupled with an energy audit to convert the engineering data to money.  Manual J gives you the apples to apples comparison of the various systems to choose from and the energy audit provides a side by side dollar comparison of each of those systems).  The highest ROI or NPV wins.   Oh yeah, it's more comfortable and it's safer too.
In the spreadsheet,  the total of the annual savings is $68,730.  Annual savings?  I must be looking at the wrong spreadsheet.  I don't think that is right.   This seems more impressive to me than a NPV of $25,934.