I like this plan - I do believe Standing Column Wells (SCW) have a place in the geo world - easier on the water supply than open loop but also possibly more efficient AND cheaper to install than vertical closed loop. A similar option is two widely spaced wells, one for supply, one for re-injection.
One clarification I see - he probably figured 2 GPM per ton, so you'd need 8-12 GPM. Here's the approximate math: 5 tons ~ 60,000 Btu per hour. A pint / pound of water takes / gives up 1 BTU per degree. If you pull 10 GPM out of the ground at 52 degrees and return it at 40 degrees, available heat is (10 GPM * 60 minutes / hour * 8.3 pounds / gal * 12 deg (52-40)) = 60,000 BTUH.
As I understood it (and I may be wrong), the nominal supply required was effectively 0 GPM, since water is being drawn and dumped at the same rate. The only time the 2GPM comes into play is when the system goes into "bleed" mode, which would happen when the standing column's temperature gets too high and it's necessary to bleed off some of the warm water so that it is replaced with cooler ground water.
But in relation to your BTU math, he also said that there was a minimum size of the water column that came into play, which essentially determines the thermal capacity of the well. I presume that this in turn interacts with the surface area of the well, which determines the rate of heat exchange with the ground.
Or is this layman missing something big...?