I am helping install a new Comfort-Aire GeoMax 2, 3 ton, open discharge system.  This is new for the heating contractor too, so I am being a guinea pig and know it.  His supplier sent two Taco valves which is fine, but also 2 hays 4gpm water controls.  Don't I need a 4.5 for the first stage and a 1.5 for the second stage making 6 total?  Why can't I just use ball valves, which could actually be adjusted to fine tune the system once it is operating?  Thanks in advance, I'm sure I'll have more questions.   
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
01 Oct 2008 04:15 PM
Can go as low as 1.5 GPM per ton if open loop water > 50 degrees. Waterfurnace does not recommend dual valves for 2 stage, FWIW.

I don't think ball valves are intended to be partially opened to regulate flow - might be ok at fairly low pressures.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
GeothermalmanUser is Offline
New Member
New Member
Send Private Message
Posts:58

--
01 Oct 2008 04:26 PM
Homeowners like to play with valves. Keep temp and pressure gauges off the system too. Use pt ports.
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
01 Oct 2008 04:42 PM
On an open system, you need to have a valve on the discharge side to keep water in the heat pump when the flow pump shuts off. This helps to reduce scaling.

2 gpm per ton is minimum flow, if you are a little over it is not a big deal.

So you need a flow controller on the inlet and a valve on the outlet.
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system