I had a geo-therm system installed in the house we built. We have the afore mentioned system for the downstairs but have a smaller 2 Ton variteck for the upstairs. Both units are supplied by two circulating pumps in series. This is a closed pond loop.

This summer the system performed great. Now however, the 20 degree nights leave a lot to be desired of this system. I have had a terrible experience with the outfit that installed the system. I feel like I know more than they do and I know squat. I found a company in another town to come bail out the original installers. They basically filled / charged the pond loop. I had them come back out two weeks ago and put another charge on the loop. For some reason, it was air bound.

I figured this might solve the inept performance of the envision unit. Then it got COLD for a couple of days. The system runs for hours and willnot get above 71 deg. Of course since I do not have zone control (didn't know, wasn't offered) our bedroom is quite cooler than that...

What I have done is checked the Y1 and Y2 terminal with referenct to the common and 24V is present when calling for stage 2 heat. Looking and reading the installation manual I found dip switches misaligned according to the book. I have placed them in the position per the book. This seemed to have allowed the fan to function on variable speed. Last night I placed a thermometer between the heat exchanger and blower. Air temp is about 81 deg...shouldn't this be near 100 deg?

Any thoughts on where to go from here? Water temp best I can tell is 49 deg.


Mike



Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
25 Nov 2008 02:24 PM
I have the same WF Envision GSHPs - my 3 and 5 ton units are on either side of your 4 ton unit.

Here are a couple of charts to give you a sense of what these units should be doing - note that it's all exclusively 1st stage operation for me.

My supply air at the moment is in a range of 95 - 96°, noting that return air is coming in in a range of 72° - 75°.  Thus, my delta air temp, return versus supply, is in a range of about 21° - 23°.

I would think you'd see something similar with your 4 ton Envision unit - again note this is 1st stage only.

A lot more info on these Envision units is available at http://welserver.com/WEL0043 .

Hope this helps.

Best regards,

Bill

Attachment: SampledSupplyandReturnAirTemps-BothUnits copy.jpg
Attachment: SampledAirEvaporatorCoilsDeltaTemps copy.jpg

Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
25 Nov 2008 02:44 PM
Posted By MSHAT1 on 11/25/2008 1:29 PM

Air temp is about 81 deg...shouldn't this be near 100 deg?



Mike


This is a definite problem.  It almost sounds like your fan is on high speed and your compressor is on low speed.


Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
25 Nov 2008 04:34 PM
Did you cycle power to the unit after making dip switch changes - or better yet, have it completely powered down when you changed the switches? Without that step, changes may not have taken effect.

I third the motion - you should have at least 20 degrees rrise in air temp across the unit, probably a bit more


Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>