Hello, can anyone tell me how many gals of antifreeze I must add for two 500 ft wells with 1 1/2 pipe. My contractor is getting two diffenent answers. One says 55 gals the other says 120 gals. Turns out my well guy didn't put the antifreeze in.
geo fan
04 Dec 2008 02:39 PM
the way I have always added to a system is to measure in water . get that gal. divide by 2 and pump out the water as you pump in the required anti-freeze . Re purge and allow the pump to run for a while to mix the solution. test for freeze protection
But Im sure somebody here knows a math formula to tell you without my additional steps
Palace Geothermal
04 Dec 2008 06:19 PM
If you have 2000' of 1.5" pipe, the total volume is 192 gallons. 20% methanol will give you freeze protection to 15°. That would be 38 gallons of methanol.
Scott9345
Thanks for the replys, I agree we decided on 40 gals. I will have to live on strip heat until next Wednesday when they can come and purge the system.