Have problem. I purchased a trane 3ton unit online but wasnot told it was only for cooling. my hvac contractor installed it and to his surprise discovered this.  he has tried to make it a heating unit also by adding a 4-way reversing valve and compressor. costed 800.00.  The aux. comes on. alot and the unit runs all the time when its below 35f. heat is set at 67f and if its 20f out it doesnt keep up. he says a 3 ton unit for a log home, if working right will do fine  due to thermal mass. i have 3000sq.ft. I think i need a new unit and a 4 ton unit. any sugg.
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
06 Dec 2008 12:06 AM
Posted By snowaway3 on 12/05/2008 11:26 PM
... I think i need a new unit and a 4 ton unit ...

Agreed.

Best regards,

Bill

Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
snowaway3User is Offline
New Member
New Member
Send Private Message
Posts:5

--
06 Dec 2008 12:31 AM
hey thanks for your input. My heat loss factor ranged from 80000 to 97000. u think 4 ton will do or would 5 tons be more effiec. I know there are many factors to consider but in general. we do burn some wood in a high effiec. insert
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
06 Dec 2008 10:26 AM
Posted By snowaway3 on 12/06/2008 12:31 AM
hey thanks for your input. My heat loss factor ranged from 80000 to 97000. u think 4 ton will do or would 5 tons be more effiec. I know there are many factors to consider but in general. we do burn some wood in a high effiec. insert

A 4 ton at best will only give you  55,000 btuh  at 50° EWT.  If your EWT is 30° you will only get  around 40,000 btuh.    What kind of loop do you have?
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system