This is a spin off from another thread.

I have a limited understanding of electricity and power and am hoping others can further my understanding.

I have a Watt Node meter that says my heat pump uses about 4800 watts when running.

I put my clamp meter on the lines running to my heat pump and measured 19.5 amps.

I measured the voltage and read  248 v

Since watts = volts x amps,   19.5 x 248 = 4836 watts.

So now I am wondering,  when measuring amps with a clamp meter on a 240 volt motor do you need to measure each leg and add them together?

If so,  my above calculation is wrong as I only measured one leg.



Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
12 Dec 2008 03:45 PM
No - 1 leg should suffice - go ahead and measure the other - they should be the same.

Watts = Volts x Amps only in case of DC power and in case of AC with unity power factor - purely resistive loads such as water heater, incandescent light bulb, coffee maker, clothes iron, etc.

Where an AC load includes motors or transformers, Watts = Volts x Amps x PF. Power factor varies from 0.0 to 1.0 depending on the nature of the load.

Neglecting power factor and calculating Watts from volts and current will lead to inaccurately high calculated wattage.

I wonder if your Wattnodemeter calculates PF and adjusts - based on your post it may not.

Hope this helps.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
12 Dec 2008 04:03 PM
Which is more likely?

The watt node doesn't adjust for PF or my PF =1 ?
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
12 Dec 2008 04:29 PM
Good question.

My understanding up until now has been that compressor motors exhibit lagging power factor - PF<1

I surfed Bill's link to Wattnode (I assume you have similar unit) and it quite emphatically stated that it adjusts for PF

So, for now, I don't know - maybe motors have gotten better about power factor lately
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
12 Dec 2008 05:33 PM
Engineer,

Thanks for your input.

My Wattnode is the same brands as Bill's.

The specs on my Heat Pump say that it should draw 4 kW. So if I add the fan and loop pumps, I guess that this all adds up.


Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
12 Dec 2008 11:01 PM
FWIW, I put my Kill-a-Watt on the house fridge - PF = 0.97 with compressor running. That supports the idea that compressor motors have become better regarding power factor
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
overlyhvac.comUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
13 Dec 2008 02:08 PM

igshpa--    dmd=  .85 X ( vx I ) for single phase

3 phase is 1.732 x .85

 

Electrical demand is then used to find eff and capacity

Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
13 Dec 2008 03:32 PM
what is dmd?
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
overlyhvac.comUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
13 Dec 2008 04:26 PM

DMD=  electric demand ( W )

engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
13 Dec 2008 09:05 PM
So, should I infer from that that a rule-of-thumb PF for compressors is 0.85?

That would be handy to know, and reconcile the amps I read for my unit against WF's specs for Wattage at my waterside conditions.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
overlyhvac.comUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
14 Dec 2008 04:33 PM

Whether it is a rule of thumb or not,,,, im not sure. It is a set value in the IGHSPA Handbook under water to air unit startup sheet to find capacity ect.

I use it to calculate capacity, cop, ect