Is a hot pre-heat tank and desuperheater LWT (125 degrees) a bad thing for a 3 ton horizontal loop Tranquility 27? It has been 12 degrees outside, and the heat pump running nonstop all day in 1st stage to maintain 70.
Regards, Masoud |
|
|
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 16 Dec 2008 09:09 PM |
|
If you are asking about turning off your desuperheater to put more heat into the house, then the answer is yes but not much. By turning off the desuperheater you will get about 3000 more BTUh into your house. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Masoud
 Basic Member
 Posts:180
 |
| 16 Dec 2008 09:23 PM |
|
Thank you. I was concerned about high water temp. Is it an indication of overworking the system? Dewayne, in one of your posts you indicted that a closed loop system should not run more than 90% of the time. Regards, Masoud |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 16 Dec 2008 09:30 PM |
|
The hot water temp is not a problem for the heat pump.
I think that the 90% number is referring to the design practice of sizing a heat pump and loop to take care of 90% of the load and letting strip heat make up the 10%.
I don't know of any problems created by running full time. Others might know more about this than me.
Have you thought about letting the unit go to second stage so it can reach set point and have a rest? |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Masoud
 Basic Member
 Posts:180
 |
| 16 Dec 2008 09:58 PM |
|
Thank you Dewayne. Yes, I can make it go to 2nd stage with supervision (manually rising the set point). But, then it starts in 1st stage again. With my thermostat automatic 2nd stage does not begin unless the room temp falls at least 2 degrees below set point. I'm sorry for misunderstanding about 90% run time. Regards, Masoud |
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 16 Dec 2008 11:21 PM |
|
I know of no issues with long run times, especially in low stage. Long run times increase efficiency and, often, comfort. Do you find you house to be comfortable and evenly heated?
The 125 preheat tank means you are getting close to if not all of your domestic hot water made by the desuper - a significant bonus.
Where are you and what is the design low outdoor temp for your system?
|
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
Masoud
 Basic Member
 Posts:180
 |
| 16 Dec 2008 11:51 PM |
|
Thank you engineer. The house is heated evenly with one zone, except when the fireplace is on. Then the back of the house loses 3 degrees. I am in SE Michigan. The winter design is -5 degrees. It seems that at current EWT, with outside temp in low teens, 1st stage is at its limit. Regards, Masoud |
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 17 Dec 2008 12:33 AM |
|
Excellent!
I'm guessing the fireplace is kinda near the thermostat and fools it into cutting out too early for the back of the house.
That 1st stage gets you into the low teens suggests high stage will carry you right down to design temperature, with plenty of hot water to boot, unless loop temps fall appreciably.
One observation I meant to make earlier is that as EWT and preheat tank temps rise, the proportion of total heat going to hot water instead of your rooms, falls. That's good, since the very long run times come with decreasing outdoor temps and increased space heating loads. Desupers divert approximately 10 % of system heat, but the specification data assumes moderate desuper EWTs, in the case of WF, Envision, 90 F. At 125 the diversion is probably more like 5% or even less. |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 17 Dec 2008 07:47 AM |
|
Masoud,
Just curious, what is your EWT? |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Masoud
 Basic Member
 Posts:180
 |
| 17 Dec 2008 05:31 PM |
|
Dewayne and Engineer: Thank you for answering my question. Dewayne EWT was 43.6 degrees today. It has been a cold December in Michigan, around 15 degrees below normal. These are temps we normally get from mid Jan to mid Feb. The early low temps now will depress EWT later in Feb, when it can still bee very cold. Regards, Masoud |
|
|
|
|
Brock
 Advanced Member
 Posts:599

 |
| 18 Dec 2008 12:18 PM |
|
Masoud, that's not bad our low EWT in Green Bay, WI is 38.8 already, definetly a cold year so far... |
|
| Green Bay, WI. - 4 ton horizontal goethermal, 16k gallon indoor pool, 3kw solar PV setup, 2 ton air to air HP, 3400 sq ft |
|
|
Farmboy
 Basic Member
 Posts:356
 |
| 18 Dec 2008 04:04 PM |
|
Masoud has a horizontal loop system, closed I assume. Brock, is your's also horizontal and closed?
Curious if those with vertical loops are also seeing descending EWTs earlier in the heating season! |
|
|
|
|
Brock
 Advanced Member
 Posts:599

 |
| 18 Dec 2008 05:16 PM |
|
Yup, horizontal closed (adjusted my profile), besides the radiant geothermal I have used 8 therms in the natural gas furnace this fall, I only seem to need the gas when it's really windy and below about 10F. |
|
| Green Bay, WI. - 4 ton horizontal goethermal, 16k gallon indoor pool, 3kw solar PV setup, 2 ton air to air HP, 3400 sq ft |
|
|