Can anyone comment on these numbers?
Last Post 06 Jan 2009 09:16 PM by geodean. 23 Replies.
RayTyUser is Offline
06 Jan 2009 05:20 PM
I was thinking about the grout that goes into the vertical holes that your loops are placed.  When using enhanced grouts you can reduce hole depth and the number of holes.  But if just a regular 20% solids is used in a system designed for enhanced grouts you will run into some serious efficiency issues.
Ray
geoSteveUser is Offline
06 Jan 2009 08:29 PM
If the heat load is 64053 BTU/hr wouldn't this require only a 5-1/2 ton unit (12,000Btuh per ton) -vs- the 8 tons (two 4 ton)? It seems like you have plenty of heat pump capacity. That would give you about 140' bore depth per ton of required heating. If all 8 tons were needed the bore field does seem undersized.
-=Steve=-
06 Jan 2009 08:37 PM
Refer to ACCA Manual S - designer must incorporate specific parameters of each individual installation - model tonnages are nominal, not actual for every condition, and low loop temperatures significantly reduce actual heat output to well below nominal ratings.
Posted By geoSteve on 01/06/2009 8:29 PM
-=Steve=-
 A 5 ton heat pump with EWT of 30° will give you about 48,000 Btuh  not 60,000.   This is a mistake easily made by new comers to the geo business.
People Online People Online: Visitors Visitors: 239 Members Members: 0 Total Total: 239