GEO Climatemaster 036 efficiency
Last Post 29 Jan 2009 04:17 PM by geodean. 9 Replies.
shaedogUser is Offline
29 Jan 2009 10:13 AM
can anyone explain the chart located in the manual.
looking at COP numbers for flow
29 Jan 2009 10:14 AM
can you post the chart?
29 Jan 2009 02:46 PM
http://www.climatemaster.com/downloads/RP812(3).pdf (page 7 036 heating)
sorry but i have not been suscsessful pasting the page.
i am curious as with a lake loop my water is 4 degrees C at bottom with ice on lake. that is close to 40 F.
how can i measure my source flow? i have 5 300 foot 3/4 poly loops fed from a 1 1/4 pipe 100 feet one way and ten feet from lake level to pump altatude. it is a grundfos 220 pump with a variable prop
positioning selector. you would think maximize this flow?
from this chart ewt = 40, ewt = 100, lwt=111.7, does this mean if i have 120 gallons that it would go from 100 to 111 in 120/5 25 minutes???
29 Jan 2009 03:07 PM
what is the 5 that you are dividing the 120 by?
the correct way to look at this is:
If you have 120 gallons that you want to raise 11° this will require 10,560 btu's ( 120*8*11)
The heat capacity of of your heat pump is at the conditions you state is 29,2000 btuh.
so if you do 10,560 / 29,200 = .36 hours = 22 min.
This is based on a flow of 9 gpm on both the source and load side. If you have P/T ports on your system, you can determine flow via the delta P across the heat pump. If you don't have P/T ports....shame on you.
29 Jan 2009 03:21 PM
the 5 was based on a flow of 5 gpm. i was just speaking with the rep. he was showing me as per the charts that i can determine the flow from the p/t ports. they only put them on the lake loop. i had asked for actual pressure guages when they were installing but......o well....
i hope they will give me two more p/t ports then i can figure this out. the source loop has nothing on it.
in your math 120 gallons 11 degrees, where did the 8 come from?
thanks eh! ;)
29 Jan 2009 03:23 PM
8 is how many pounds one gallon of water weighs. good luck
29 Jan 2009 03:34 PM
thanks
i mean the load side has no ports. but, looking at the curves is the presure drop across the unit like the lake loop/ the lake loop p/t ports are imediately outside the unit. to install the p/t's on the load side i would imagione the same?
will these pt ports measure such small psi?
29 Jan 2009 03:46 PM
yes  ...the P/T ports  go just out side of the unit.   You need a pressure gauge to measure the psi
See attached
Attachment: Resize of Gauge.jpg
29 Jan 2009 04:10 PM
my supplyer is geting me two more p/t ports to install on the load side.
he has a "kit" he said i can use to do my measuring. my concern is that looking at the charts the load side presures are quite small.....meaning accuracy?
i would guess then that the temperature is also very critical. i think or hope his kit would provide both as it is a p/t port or do i need to plug two things in. guess i need to see the kit
fun...this is....
Posted By shaedog on 01/29/2009 4:10 PM
fun...this is....
the numbers on the chart are the pressure drop across the coil, not the actual pressure you will be reading.  So you are looking for a difference in pressure of 1.1 pounds from In and Out.
Maybe you understand this,  yes you will need an accurate gauge to show a 1.1 psi delta.
People Online People Online: Visitors Visitors: 142 Members Members: 0 Total Total: 142