Posted By engineer on 02/08/2009 12:24 PM
Does the Rheem Powervent not deliver heat to the very bottom of the tank? Coventional old-tech center chimney gas storage water heaters apply the flame to the very bottom of the tank. If the Rheem does not, that could allow a chunk of cold water to exist there and give the DSH something to work off of.
Another explanation is R22. That plus another clue - that your hot water temperature rises during heavy DSH seasons suggests that the DSH has much hotter compressor discharge gas to work with. Is your CM a single stage? I've seen / heard of single stage R22 units with hot gas temp close to 200 F. Lack of a TXV in older systems may give rise to more superheat, depending on charge, and that contributes to higher compressor discharge temp as well.
In low stage my 410a unit's hot gas discharge line is not much hotter than what I can hold onto with bare hands - maybe 140 or so.
I've never doubted your numbers and success with single tank DSH, just trying to understand why it flies in the face of experience of others - now I think I understand better.
The coaxial heat exchanger in the drain tap is definitely a few inches below the tank's burner and feels cold when the heat pump isn't running (spring/fall etc.). The GSHP contractor selected the tank presumably based on prior experience with this setup and, for us, it has worked very well.
The heatpump is single stage, but it definitely has a TXV and the DSH is limited to 125F - I believe the thermostat on the hot water tank is set at 50C (just over 120F). The water is hotter when the DSH is running (and we had pretty much continous heatpump running in January with the average temperature in the -13C range), though it's not in the 200F range!
Paul.