Dave, I started out the same as you - temperature and pressure guages inserted into P/T ports installed at EWT and LWT GSHP locations.
It became obvious pretty quickly that the information from the guages is 'noisy' - i.e., there's a lot going on such that the values move around quite a bit. And thus while there's a lot to learn from the instanteous values, there's equally plenty to learn from historical and statistically sampled values.
I suspect a significant contributor to your situation is simply inability to get the data you need to draw conclusion on your bore hole field performance, assuming you have a well performing GSHP unit and bore hole field.
A key item to keep in mind is that even as EWT may vary quite a bit on an instantaneous basis, due to the response lag of the bore hole field to sink/source the heat, the delta-T across the GSHP water-to-refrigerant heat exchanger stays much more steady. For example, for the period of cooling centered at about 15 hours ago, even though EWT is moving around quite a bit due to bore hole field heat sink lag (
http://welserver.com/cgi-bin/plot/WEL0043/InstantaneousEnteringWaterTempsEWT.gif - blue line), delta-T is much more steady, at between 4.5 and 5.5 °F, as seen here:
http://welserver.com/cgi-bin/plot/WEL0043/LoopWaterDeltaT-CoaxHeatExchangers.gif (blue line again). And my delta-T would be even less variable if it weren't for the influence of another GSHP unit connected in parallel to the same water loop (black line).
What's really instructive is look at the performance of the water-to-refrigerant's BTU output (Heat of Extraction - HE and Heat of Rejection (HR)). This eliminates getting too caught up in the very noisy EWT values, and the somewhat noisy delta-T numbers. Here, for my units, HE and HR is very steady:
http://welserver.com/cgi-bin/plot/WEL0043/SampledLoopKBTUperHr.gif . My two units are removing heat from the structure (rejecting to the earth) at rates of about 50 and 30 KBTU/hr for my 5 and 3 ton units respectively (both running at 67% in first stage only).
Given that I can see HE and HR, the more noisy EWT and delta-T values are not as valuable as predictors or indicators of problems.
All of my charts are visible, real-time, at
http://welserver.com/WEL0043/ . There are others on this forum, much smarter than me, who also have monitoring capability, using the same system, such as geodean, at
http://welserver.com/WEL0114/ . And here's a map of a number of very creative implementations of the same monitoring system:
http://welserver.com/ww/ .
And here's info on what I'm using, overall, at
http://www.ourcoolhouse.com/index.htm , and specifically at
http://www.welserver.com/ .
Hope all of this helps.
Best regards,
Bill