Can hydronic-radiant floor benefit from geothermal?
Last Post 07 Aug 2009 10:06 AM by jonr. 10 Replies.
toffeeUser is Offline
30 Jul 2009 12:39 PM
Hi guys, please tolerate my newbie questions, first time poster here.
The way I understand hydronic-radiant floor system works is that:
  1. water heated by broiler or water heater to say 180 deg.
  2. hot water pumped into tubes under the floor though out the house.
  3. cooled water return to broiler/water heater to be heated and pump back to the tubes.
  4. I believe water returning to broiler ought to have temp higher than 55-60deg?
Questions:
  1. How can a traditional hydronic system benefit from geothermal if the return water temp is higher water circulating from the geo system?
  2. On hot days, is it possible to circular cool water from geothermal system through the radiant tubes?  If the temp is say 100 deg, cool water ought to cool the room down some?
  3. How much can (2) cool the room?
  4. What about moisture or water condensation under (2)?  So a dehumidifier would be needed?
I am just puzzled.
30 Jul 2009 03:01 PM
Posted By toffee on 07/30/2009 12:39 PM
Questions:
I am just puzzled.
First off, it's a boiler not a broiler (unless you have your radiant cranked up to ~800-1000F :-) ).
Most radiant floors using concrete slabs never see 180F water.  In fact, many radiant staple-ups under wood floors (often retrofits) don't have to see more than 140F even when it's super-cold out, assuming a reasonably insulated house in a non-arctic environment.  Radiant slabs can often be designed to run at temps under 100F even on "design day" and much cooler during average heat loads, making them suitable for geothermal.  The return-water temps are set by-design, a function flow rate and heat given up to the room.  Delta-Ts of 20F or more are common, (120F out 100F return, for an average of 110F, etc) but return temps will always be above room temperature while in heating mode.
Traditional hydronic systems run at much higher temps than radiant in order to use less radiator. With radiant you have a very large surface area built-in, reducing the temp need to transfer the heat into the room.  Old-skool stuff typically ran 160-200F out, 140-160F returns.  Cast iron boilers and ceramic/masonry lined flues demanded that return temps never drop much below 140F in order to avoid potentially destructive condensation, so there was little incentive to design-in more radiation for lower temp returns, but it's almost always possible to get there with 1.5-2x the linear feet of fin-tube baseboard (or cushy panel radiators.)
Stainless steel flue liners can reduce the minimum safe return temp requirement to ~130F for natural-gas or propane fired cast iron boilers, but below ~122F corrosive condensation begins to occur on the heat exchanger plates. (Oil-exhaust condensate is significantly more corrosive- it'll eat almost anything.)  Copper water-tube boilers can safely run down to around 100-110F, but modern condensing boilers (and tankless HW heaters) have heat exchangers designed tolerate arbitrarily low return water temps.  Since radiant output temps are often lower than the minimum return-water temps of tradtional boilers, copper tube & condensing boilers are better choices for radiant designs than trusty tried & true cast iron beasts (even though there are several ways of plumbing outputs & returns to keep return temps up to the necessary minimums while delivering appropriately low temps to the radaition, if need be.)  At low enough radiation temps, heat pumps work too- most slabs can be made to work with geothermal.
Radiant cooling using floors works, but not nearly as effectively as radiant cooled ceilings or walls, since the cool-air puddles at the floor forming an insulating boundary layer, whereas with radiant cooled walls & ceilings significant convection is induced and currents of warmer air come into contact with the cooling surface.  Condensation is an issue only when the dew points above the temp of the cooling surface.  Since radiant floors have to be chilled significantly more than walls or ceilings at the same cooling load that's where you're more likely to run into condensation issues.
In much of the eastern US the latent load (humidity) is a significantly larger AC load than the sensible (temperature) load, and mechancal dehumidification will be necessary for comfort & health.   For instance, right now the dew point outside my office window is over 70F.  With an indoor temp of 76F that would translate into ~82% relative humidity, which is damned uncomfortable and prime growing condtions for mold/fungus on building matierials.  Radiant cooling surface temps would be limited to 70F right now as well, meaning it's efficacy (particularly on a floor) would be limited.   Here in New England, some mechanical dehumidification would will be required, even more-so in Georgia/Florida, but in Arizona/ Nevada you can chill it to your heart's content without much fear of condensation or clammy-discomfort.  (Evaporative coolers are fairly common there, intentionally raising the RH as part of the cooling process.)
As with radiant heating, how much you're able get out of radiant cooling depends on the number of square feet of chilled surface you have to work with, and the water temps needed to achieve the necessary heat transfer.
Bill NeukranzUser is Offline
30 Jul 2009 03:22 PM
I learned a lot of stuff I didn't know from this one post.  Thanks for putting forth the time to publish your comments!
06 Aug 2009 11:36 AM
Posted By Dana1 on 07/30/2009 3:01 PM
Questions:
I am just puzzled.
[/quote]
First off, it's a b[u][i][b]o[/b][/i][/u]iler not a b[b][i][u]r[/u][/i][/b]oiler (unless you have your radiant cranked up to ~800-1000F :-) ).
Stainless steel flue liners can reduce the minimum safe return temp requirement to ~130F for natural-gas or propane fired cast iron boilers, but below ~122F corrosive condensation begins to occur on the heat exchanger plates. (Oil-exhaust condensate is significantly more corrosive- it'll eat almost anything.)  Copper water-tube boilers can safely run down to around 100-110F, but modern condensing boilers (and tankless HW heaters) have heat exchangers designed tolerate arbitrarily low return water temps.  Since radiant [i]output[/i] temps are often lower than the minimum return-water temps of tradtional boilers, copper tube & condensing boilers are better choices for radiant designs than trusty tried & true cast iron beasts (even though there are several ways of plumbing outputs & returns to keep return temps up to the necessary minimums while delivering appropriately low temps to the radaition, if need be.)  At low enough radiation temps, heat pumps work too- most slabs can be made to work with geothermal.
I am still unclear how Geothermal can benefit hydronic radiant heating, would appreciate if you could elaborate.
heatoftheearthUser is Offline
06 Aug 2009 01:49 PM
geothermal systems utilize heat pumps that transfer heat from one place to another, In other words the water thats traveling through the ground does not circulate through your floor, it just circulates through the heat pump where heat is extracted, and transfered to your radiant floor loop. In a radiant floor system a water to water heat pump is used. Those heat pumps supply water temps are in range with the water temps used in radiant floor systems, unlike a traditional boiler where mixing valves are used to bring down the temp (from baseboard temps to radiant floor temps)
06 Aug 2009 02:38 PM
Thanks heatoftheearth.  How efficient are the water to water geothermal heat pumps as compare to the current boilers?
06 Aug 2009 03:02 PM
Efficient in dollars? Depends on fuel used and costs, but maybe 3x more efficient.
If I were going to try this, I'd use ceiling  fans to promote convection and make sure that the floors are concrete or tile.
06 Aug 2009 05:40 PM
Gee, I didn't elaborate enough already? :-) I'll try to keep it simple.
Geothermal (as in ground-source heat pumps) can move heat efficiently from the ground to raise the temperature of the heating system's circulating water. But at water temps over 100F the efficiency of the heat pumps starts to fall off, considerably, and over ~110F it's not very efficient at all, and other methods need to be considered. Radiant slab floors (concrete materials) can run at temps under 100F most of the time. Radiant wood floors usually need higher temps. But the temps either actually need are a function of actual winter temperatures and the insulation levels in the house. If you can design the house & slab that sufficient heat gets delivered to the room via the slab on the coldest day of hte winter at under 110F, geothermal heat pumps can be a reasonable way to heat the water in the radiant loop. If not, look for other heat sources (like boilers.)
Heat pumps can move ~200-300% more heat energy than the electrical energy that drives the pumps. But purchased electrical energy is typically more expensive that other sources (but this will vary, a LOT!). From a source fuel point of view, a coal & gase-fired plants delivers only an average ~28-35% of the energy to the load (the heat pump), with the rest going up the flues and heating up the transformers & transmission wires, so at 300% pumping efficiency the heat pump is only delivering ~75-100% of source-fuel efficiency. Gas fired heating boilers deliver 75-90% average efficiency, in some instances slightly more. Whether a condensing boiler is more source-fuel efficient than a heat pump or conversely depends on a whole lot of particulars, but in many or most instances the heat pump wins.
ecobuilderUser is Offline
07 Aug 2009 01:06 AM
I am using a geothermal heat pump to not only heat the radiant slab of my last project but cool it as well. The cooling is working much better than hoped and keeping the house at a comfortable 70F. we also installed a whole house dehumidifcation system to control the humidity levels in the house. I has seen this done in ceilings and chilled beam set ups as well but if you don't control the dewpoint then condensation will occure and I have seen one house ( built by others) that the chilled beams were more like shower units with water dripping steadily and a catchment drain system was needed to resolve it. My project used the concrete floor as the finish, which did several things to boost efficiency, like no R value to resist heat flow. Also when in cooling mode if condensation does occure it will not damage the flooring. The thing the homeowner really likes about it is that you don't even know the AC is running, no noise, no cold air blowing around just a steady comfortable controlled envirornment. Some of the other considerations when cooling with this methods is the total capacity of the floor to absorb the heat and move it out of the building. You can only get about 10-15 Btu's/sqft out of it, so if your house isn't designed with really low heating loads this won't work correctly either.
as far as heating the slab with the geothermal water-water heat pump this did this with easy and the monthly cost to heat this home here in MA was about $50-60/month ( $.17/Kw/Hr) during this past Feb and March. The two really play nicely together once you have tweaked the system and flow rates to keep the pump cycling correctely. I am supplying the water to the slab at about 90-95F much lower than almost any other method of heat delivery. How efficient the pump runs is reliant one several factors, Hp enter water temperature, flow rates, pressure drops and delivery rates and temps. The closer the entering water temperature and the delivery temperature are the more efficient the system will run.
Also reducing the heat losses and gains from the house before designing the heat pump system is another way to make these systems less costly by reducing the size of the system and the ground exchange. Many times the efforts to conserve or reduce the need for heating and cooling are less costly than putting in a oversized heat pump in an inefficient home, that will not give you the results you are looking to achieve.
Tom Pittsley
www.eebt.org
"Don't be afraid to go out on a limb. That's where the fruit is." Jackson Brown
07 Aug 2009 09:57 AM
Posted By ecobuilder on 08/07/2009 1:06 AM
Tom Pittsley
www.eebt.org
Yep- in MA the latent loads are many times the sensible load.  Dehumidification represents the lions-share of air conditioning here, which makes chilled slabs/walls/ceilings/beams alone inadequate.  When dewpoints are in the 60s & 70s Fahrenheit the chilled surfaces will be continually wet, but won't reduce the RH much.  Keeping the RH under 65% is critical to keep mold under control, keeping it under 60% is usually more comfortable. Those with dust-mite allergies need to keep it under 50% to keep the mites from reproducing.  The tighter the house, the more important whole-house humidity control becomes, independent of season.
And yes, lowering the heating & AC loads by thermal envelope & fenestration design dramatically reduces the size & cost of the mechanical systems require to handle those loads (not to mention the cost of operation!)  But as the loads get smaller the complexity & efficiency of radiant or geothermal become less relevant, and rationale for the up-front cost of highest-efficiency systems more difficult.   For instance, the Urbana IL PassiveHouse uses a kilowatt restive element in the ventilation airstream as it's heating "system"- far less efficient than a geothermal heat pump & radiant slab, but who cares?  High efficiency building envelopes are ultimately more important than high efficiency heating/cooling systems in terms of environmental impact.  But as retrofit on existing structures, high-efficiency systems often have lower upfront cost and are easier to implement than envelope upgrades of equivalent impact.
> installed a whole house dehumidification system to control the humidity levels in the house
The issue I have with doing this is that a typical dehumidifier is an air-conditioner where the heat is not exhausted. So you are cooling air, heating it back up, then cooling it again.
Better if the water from the heat pump was first used to cool the air for dehumidification and was then pumped through the loops.
People Online People Online: Visitors Visitors: 264 Members Members: 0 Total Total: 264