On a previous post, the home owner stated the heat load was 48K BTU/HR. Now here is the question. Do you size the loop for the unit or for the heat load? If the unit, why? If the heat load then why?
A 3.5 ton unit (about 52K BTU) should be right for the 48K load). Of course, a 3 ton unit with some minimal use of back up heating might be optimal - especially if the cooling load tended to be really low - say 24K BTU/hour.
If you install a 3.5 ton unit would the loop be sized different than for a 4 ton unit? If yes why since the larger unit just cools the house faster. The water temperature might get a tad cooler due to faster heat extraction but on the other hand it might not since the compressor would be providing more heat. If the heat load is 48K BTU / hour does it really matter if the 3.5 ton unit runs 55 minutes or if the 4 ton unit runs 48 minutes? The extra 7 minutes of no heat transfer should let the heat disappate.
Thoughts? Comments? Observations? Snide remarks :) |