System Lockout Alert
Last Post 12 Jan 2012 12:17 PM by geome. 31 Replies.
geomeUser is Offline
22 Dec 2009 07:56 PM
When a geothermal system locks out in heating mode, backup or auxiliary heat can be engaged and mask the problem until you happen to notice there is a problem by:
looking at the unit and see a fault light;
possibly see a system monitor error on your thermostat (if so equipped and wired);
notice that the system sounds different;
notice the smell of burning dust coming off the heat strip wires;
or get an extremely high utility bill.
I'd rather find out as soon as possible so I can either correct the problem (if I can) or call the installer.  I can't be the only person interested in having a more obvious alert when their system locks out.  Even if I am, I'd still appreciate suggestions.
I have a 24vdc terminal on our equipment that is energized when the system locks out.  Maybe have this power a buzzer, light, a relay, something that shocks the dog every 3 seconds (just kidding).  Any suggestions?  Maybe a buzzer with a volume control?
22 Dec 2009 08:48 PM
I've had one lockout event. An outside worker mistook my open loop drain line for a garden hose left running, found a valve I shouldn't have included in the system, and closed it. Thermostat alerted wife to condition while I was out of state. I talked her through finding the valve, reopening it, cycling power to the geo, and all was then well.
Bill NeukranzUser is Offline
22 Dec 2009 09:35 PM
Posted By geome on 12/22/2009 7:56 PM
... I have a 24vdc terminal on our equipment that is energized when the system locks out.
I'd be careful here.  It may be a 5 VAC signal.
One way to check is to reroute a wire, that ordinarily passes through the Comfort Alert, around the Comfort Alert, rehook it up properly, and then start the system up.  This will deliberately trigger the signal from the Envision's LO terminal.  Get a volt meter and determine if it's AC or DC, and how much voltage.
WaterFurnace's documentation says 0-5 VAC.
G.O. JoeUser is Offline
23 Dec 2009 06:37 AM
You are correct. I confirm that the LO signal from the Envision board is per their documentation 5vac.
I believe most solid state relays used in modern control boards and thermostats are rated 5vac to 32vac. At the very least I believe with good design they should be able to operate at various voltages and protect themselves from backfeeds. For fear of releasing the factory installed smoke, you could run the LO 5vac signal thru a relay to isolate the Thermostat from the control board. This isolation might already be built in but I have no way to confirm at this point.
WF absolutely wants you to buy their branded thermostats and will not provide tech support for others. Honeywell should step up here and provide support unless they want it known that their latest and greatest thermostat doesn't work with WF.
Geome
The problem perceived here is the HW Prestige "feature" that turns the L input into an output when put in Emergency Heat mode. What will happen when that 24v gets sent back to the unit control board? It depends on the unit. If the unit supplies a 24vac L lockout signal anyway and the signals are in phase (they will be if they come off the same transformer) it is the same signal so it doesn't matter.
I contend with the Prestige (will confirm later) if you are in comp lockout and your aux is not locked out you would not necessarily manually change to Emergency (it doesn't happen automatically). You would-
1- Notice it is a little cooler than normal (the Aux is working at 3rd stage setpoints)
2- Put your bathrobe on (because of #1 and it usually happens at 4 AM)
3- Look at thermostat and notice you are in lockout
4- Remember to notate lockout codes at unit (and confirm nothing catastrophic has happened (ie smoke, water leaking, or iceberg hanging off unit etc)
5- Perform a soft reset at the thermostat by turning thermostat off for a few moments and back to original settings
6- Confirm heat is coming out and go back to bed hoping it doesn't happen again (if it does just stay in bed. It may be a couple of degrees cooler than you want but that's OK because you are paying full price for your heat right now)
7- Call for Qualified Service
At no time have you put the thermostat manually into Emergency heat mode activating the dreaded L output from your Honeywell Prestige. Besides if you did you would be doing a soft reset of the comp lockout by removing any calls to the control board and your installer will not appreciate that (he would most probably prefer to read the codes and conditions him/herself).
Emergency heat only has to be selected when you know the compressor and or related systems have failed and you do not want to call for their activation. At that time the L wire at LO connection (whether relayed or not) could be removed and capped until the system is repaired.
23 Dec 2009 03:56 PM
Thanks for the correction. This is from the WF Envision Installation Manual: "Thermostat Selection - Configures the control for a pulsed lockout signal (ComforTalk and FaultFlash thermostats) or continuous 5 VAC lockout signal."
The Prestige output voltage is not listed in the Prestige manual, only that there is output when the system is in emergency heat mode. From the VisionPro manual, the VisionPro has a 24 VAC output when the system is in emergency heat mode. I don't know if this is the same for the Prestige.
In another area of the Prestige manual, it describes the L terminal as a "Heat pump reset (powered continuously when System is set to Em Heat; system monitor when set to Heat, Cool or Off)." I hadn't noticed this wording (including the word "reset") before since it is on another page of the manual.
I'm working with the installer to get the Prestige alert working with him since the thermostat is still under warranty. Would still like specific input from anyone here on audible methods of alerting a person to a lockout. Our installer told me that some of his customers wait until they get a $600 electric bill before noticing or calling about a lockout.
23 Dec 2009 05:19 PM
Geome
This should get your attention! You can wire it right inside box and still hear it several floors away and the right voltage too. Just remember I told you it always happens at 4 am.
http://www.jameco.com/webapp/wcs/stores/servlet/ProductDisplay?langId=-1&storeId=10001&catalogId=10001&pa=1956776&productId=1956776&keyCode=WSF&cid=GMC
23 Dec 2009 06:19 PM
Great find! Is the Maximum Supply Current of 1.5 mA ok? I'll try to find a local company that has them since they want $8.50 to ship, but beggars can't be choosers, so I'll go with them if necessary.
4 am is ok to save me aux heating costs! I will definitely wire in a switch though, so the wires won't be ripped out by some half awake mad-man or mad-woman, (well, hopefully not).
What is the easiest & safest way to force a lockout?
Bill, I didn't quite follow all of your instructions: "One way to check is to reroute a wire, that ordinarily passes through the Comfort Alert, around the Comfort Alert, rehook it up properly, and then start the system up. This will deliberately trigger the signal from the Envision's LO terminal." So, I should disconnect any Comfort Alert wire, and route it where before re-connecting it? Thank you.
23 Dec 2009 06:45 PM
Posted By geome on 12/23/2009 6:19 PM
... What is the easiest & safest way to force a lockout?
If you look carefully at the CA, you'll see that most wires route *through* it, versus connect to it.
Simply select one of the wires that passes through the CA, disconnect it at wherever a convinient connection point it, pull it out of the CA, and hook it back up to it's original connection point.  All you've done is essentially rerouted the wire around, versus through the CA.
This will force a 5 VAC signal at the Envision's LO terminal at system start up.
I thought I saw a comment from you that you're not real comfortable with electricity, or something to that effect.  If so, this definitely isn't something I'd recommend you try to do.  Without proper precautions, such as removal of jewelry, wearing shoes, turning off power, etc., it would be easy to electrocute yourself.
And don't forget where you disconnect a wire from - reconnection at the wrong place could easily damage the unit.
23 Dec 2009 06:57 PM
Thanks Bill. I've put in outlets, changed switches, etc., but I still keep a healthy respect for electricity. Guess having a few drinks for some courage isn't a good idea before hand (JUST KIDDING!!!). How much of this should be done with the power off vs on? I assume the system should be "off" until everything is reconnected. Are any wires running through the Comfort Alert more forgiving than others (lower voltage)?
Has anyone heard from Joe? It's been a while since I've seen a post from him.
23 Dec 2009 09:09 PM
If it was me, I'd turn off the power at the disconnect next to the unit, to be on the safe side.  When you turn it back on, you'll have to wait for appropriate start up delays.
In fact, if it was me, I'd check for absence of 240 VAC after turning off the disconnect, just to make sure.
The wires that pass through the CA are all wires that go to / from the compressor.  It shouldn't make any difference which one you choose.  I'd choose the one that's easiest to mess with, and is easiest to connect / disconnect.
Be careful.
23 Dec 2009 09:16 PM
geome
First I was half kidding about the buzzer. It puts out 90db. But if that is ok with you.
Don't do anything with the ComfortAlert. I has its own communication protocol with the envision control board. The control board interprets the signal from the CA and the control board decides to lockout or not. The buzzer just gets wired between LO (lockout) and C (common).
The easiest why to force a lockout without subjecting the unit to any stress is to short the condensate overflow sensor to ground. I know yours is a split but the connections are still there.
-With power off connect a jumper wire from terminal #12 connector block P6 (it is a 16 space block with nothing connected to it) on the Envision control board -to- terminal #14 right next to it.
-Power unit and cover your ears (I'm not sure you might have to wait for a compressor call).
23 Dec 2009 09:25 PM
Posted By G.O. Joe on 12/23/2009 9:16 PM
GOJoe, very helpful to know!  Much safer.
Many thanks!
geotekUser is Offline
24 Dec 2009 07:44 AM
If you pull one of the black wires from the high pressure switch you will get instant lock out
(no fault retry). I suggest you power down the unit before removing wire.
Have fun trying to read L voltage because my fluke 12 could not read it. High impedance  DC output. There is no useful voltage there to operate a relay. However WF has ARB board that can read the L signal and has a low voltage set of dry contacts SPDT.
24 Dec 2009 08:41 AM
Posted By geotek on 12/24/2009 7:44 AM
Interesting.
Not surprised.
I learned a while back, when I first installed my WEL monitoring system, that there's a DC component of some kind on the Envision's tstat wires (Y1, Y2, etc.).  Finding this forced me to scratch my initial design for interface to these terminals.  Instead I went to a full isolation design (24 V relays) (which continues to work fine).
Thanks for tip on how to easily force a lockout without impact to the unit.
12 Jan 2010 11:34 AM
Our installer called me back. He was unable to obtain a consensus from Honeywell and Water Furnace on how to wire an alerts and guarantee that there would be no problems with their equipment. Our installer suggested, as was also suggested here, isolation relays to avoid any potential problems. To save a few bucks I will have this done at the same time as our spring check in March or April.
Does anyone know if one relay could send power both to the alert system on the thermostat, and also to a buzzer (or would two relays would be needed)? If one relay, would it be a special type? Where would I get such an animal? I'm not very familiar with relays and wiring of this type. Thanks!
I'll also ask about the ARB board when I speak to the installer again.
17 Feb 2010 01:53 PM
The installer was out today to check on our split system noise level. Unfortunately, nighttime is when the noise is much more noticeable due to lower ambient sounds, so we are not doing anything beyond switching the T1 and T2 lines at this point.
While he was here, he installed ARB boards on both our units. The boards are small things, maybe 1" wide x 3" long. The alert on the first floor thermostat is working well. The alert on the second floor thermostat is currently not functioning due to a broken wire running from the air handler to the thermostat (the old thermostat wire was used.) Next month, the wire will be replaced when they come out for a spring check.
I plan to buy 2 voltage appropriate buzzers and switches to use as well so I will be audibly alerted if either system locks out. The switch is so I can turn off the buzzer after I am notified of the lockout (and so I won't be tempted to rip the buzzer off there is a lockout in the middle of the night and the buzzer goes off.)
17 Feb 2010 05:20 PM
24V AC sounds like a good number to me.
17 Feb 2010 06:35 PM
geotek,
I agree. Would the buzzer that G.O. Joe found for 5 VAC (when we thought we would need a 5 volt buzzer) still be ok to use?
https://www.eio.com/p-18045-velleman-tv1-piezo-transducer-5vac-40khz-85db-lead-type.aspx
The Typical Operating Supply Voltage is 5VAC, but the Maximum Operating Supply Voltage is 28VAC. I know 24 is between 5 and 28, but since 24 is at the upper end I wasn't sure if the buzzer would be more likely to go bad. Would I be better off with a buzzer designed for 24VAC? I'm just trying to do this once and get it right the first time.
Good recommendation on the ARB, by the way.
18 Feb 2010 08:56 AM
Use the R and C terminal on the unit or thermostat 24V AC all the time.
I don't know where he got 5V AC but you don't want it anyway.
You can break R through the ARB to power you buzzer.
KISS rules.
18 Feb 2010 10:16 AM
I may not have explained this well. The ARB is completely hooked up and is providing 24 VAC on the output side. Upon re-reading the buzzer manufactures specs, I see that they state operating voltage is 3-28Vac, so this one should be fine. (Low voltage AC buzzers don't appear to be nearly as common as DC.)
The 5Vac came from the idea of hooking up the buzzer directly to the LO terminal, but decided to go with the ARB instead to safely connect the thermostat alert as well. Thanks to all who contributed.
People Online People Online: Visitors Visitors: 742 Members Members: 0 Total Total: 742