My GeoMax 2 Heat Controller GSHP also this past winter went into lock-out mode due to low water temperature. By coincidence, it's the same lock-out code (4) as your Tranquility. I don't have a light on the thermo that tells me there's an error, though...I found out the difficulty way. Low Water Temp, I believe, is same as my Low Entering Water Temp code. That is, the coolant coming in from the ground loop is below the recommended temperature for the HP to operate. If the loop isn't picking up enough heat from the ground, the HP shuts down the loop and compressors to protect them from too-cold liquids. I think my minimum is 30 F. The system should AUTOMATICALLY switch to aux heat to continue to provide you with heat, though. Is it doing this? Also, my system will automatically restart itself every so often to see if the loop temperature is back above minimum. The exact causes of low loop temperatures include, (and others, please correct me/add), low coolant levels in the loops, low pressure, not enough anti-freeze, malfunctioning loop circulation pumps, poor ground conductivity, incorrect loop sizes, and probably more. Unfortunately, nothing the average lay person can fix. |