Posted By joe.ami on 09 Apr 2010 09:28 AM
I confess the thought of installing a split system that (used propane), with my torch and piston driven vacuum pump, holds little appeal to me.......
Joe,
Your suggestion sounds particularly valid and reasonable to someone unfamiliar with working with flammable refrigerants (or, to be more accurate, refrigerants that are more flammable than current refrigerants). I hear this all the time.
The reality is quite different, however.
Firstly, installing a propane-based split system is made straightforward by any one of a number of approaches. If brazing is required, the only precaution that needs to be observed is to vacuum the system first.
Secondly, regarding vacuum pumps: to understand the matter properly one has to recognise that hydrocarbons are only flammable when the correct ratio of air is mixed with the hydrocarbon (approx 2% - 10% in air). Any other concentration is non-flammable. Secondly, you must have a sufficiently powerful source of ignition.
So, back to the vacuum pump itself: what is it sucking from the circuit? hydrocarbon only. That means the internal volume of the vacuum pump, the suction side lines and all the outlet lines right to the point where the outlet ends, is non-flammable.
Let's take it to an extreme... suppose you are vacuming a propane system and decided to light a match and hold it over the outlet of the vacuum pump. What would happen? You would get a little pop and perhaps a small jet of flame or perhaps a bunsen-burner like continuous flame (depends on the vacuum pump rate and other factors) and that is all. Why? Because the flame cannot propagate back up the lines because further upstream there is no air, therefore no flammable mixture.
This principle of flammability of hydrocarbons is what makes gas burners possible. Similarly, if you take a cigarette lighter to the outlet of an open valve of a propane cylinder, the flame cannot propagate back into the cylinder and cause it to explode. No air.
Ahhh... but what about if some fool has accidentally permitted air to enter into the circuit prior to vacuuming. Firstly, it would need to be a fair amount of air in order to dilute the hydrocarbon to 2% - 10% concentration to cause a flammable mixture, but yes in that case you would have a potentially very catastrophic situation - something akin to a 'pipe bomb'.
BUT - and I can't stress this strongly enough -
if the circumstances were repeated with, say, R134a (a common fluorocarbon refrigerant that I'm sure you are aware of), then you would STILL have a pipe bomb on your hands. So called 'non-flammable' R134a is highly flammable when mixed with air above atmospheric pressure. This is not something that the fluorocarbon manufacturers like to publicise much, for obvious reasons.
Also, if brazing around common fluorocarbons, you need to be carefully aware of the potentially lethal toxic fumes that will be produced if the refrigerant or lubricant is exposed to the flame in sufficient quantities. Brazing flames on R12 produce mustard gas (you may recall this as one of the earliest chemical weapons). There are many dead refrigerant technicians giving silent witness to this. If you braze a system and the torch hit's some PAG oil, you're at serious risk. In contrast, a mineral oil + hydrocarbon system produces no such toxic fumes.
Finally, most countries now prohibit the brazing fluorocarbon systems without first recovering the charge so as to minimise harm to the environment.
So, in summary then, the procedures for safe brazing of hydrocarbon systems are the same as current procedures for brazing fluorocarbon systems, and the explosion risks for both hydrocarbon and fluorocarbon systems are actually very similar.
Additionally, vacuum pumps specifically designed for evacuation of flammable gases are readily available. These models, by design, guarantee the pump is incapable of providing ignition even if a flammable mixture did exist within it.
Posted By joe.ami on 09 Apr 2010 09:28 AM
"These pr*cks are using these technical committees as a tool for keeping naturals out of their markets."
Industry "watch dogs" that put their own interests ahead of public good? Say it ain't so!
Forgive my frustration. We're not the only industry that is on the receiving end of these tactics by monopolists/oligopolists.
Microsoft, big pharma, big banks.... it's all too common these days.
Cheers
John W Clark
Technical Advisor
HyChill Australia Pty. Ltd.