PEX loop spacing with GHP
Last Post 15 May 2010 08:33 AM by Rovic. 10 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
RovicUser is Offline
New Member
New Member
Send Private Message
Posts:11

--
12 May 2010 01:28 AM
What is the recommendation for PEX loop spacing when using a ground source water to water heat pump. I've been told that because the geothermal water source is a lower temperature (max 100 to120) then the spacing should be 6" on center throughout rather only around the perimeter. Any help greatly appreciated as I do not want to oversize the system.
BergyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:277

--
12 May 2010 01:43 PM
That depends on the Btu requirements for each room at design temperature and what types of floor covering wiil be used.

Bergy
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
12 May 2010 08:16 PM
Definitely take a whole system design approach. No one parameter (tube spacing, water temperature) suffices to design a system. Room by room and whole house load analysis coupled with careful consideration of floor coverings are all required to ensure an efficient and effective system design.

Selecting geo for radiant can be an excellent marriage, but special care must be paid to design water temperature to make the marriage work.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
RovicUser is Offline
New Member
New Member
Send Private Message
Posts:11

--
12 May 2010 10:06 PM
The house is 5300 sq. Ft 2600 on each floor. Lower floor will have a concrete over-pour to embed the 1/2' pex. Upper floor, most likely gypcrete or similar product. All floors will be tiled. Approximately 50% of each floor will be an open flow (no doors) although each floor will be separated by doors. An initial Heat Loss calculation came back at 81,000 per hour, lots of windows on top of a hill.!!!!

Rovic
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
13 May 2010 08:15 AM
Where is this particular hill located?
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
RovicUser is Offline
New Member
New Member
Send Private Message
Posts:11

--
13 May 2010 11:34 PM
Nova Scotia Canada
RovicUser is Offline
New Member
New Member
Send Private Message
Posts:11

--
13 May 2010 11:41 PM
I'm a little suss about the heat loss ( only one so far ) as the house has all new Double pane, Low E, Argon gassed windows with 4" ridged Blue poly in all cavities as well as the ceilings. I'm being quoted on 2 GHP's to cover the heat loss. Makes it expensive.!!!!!

Rovic
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
14 May 2010 10:14 PM
For $50 US you can obtain a 60 day license to use HVAC-calc and run your own load calc.

81 kbtuh is a fairly high heat load, but that's a big house in a cold place, and so far north it'll take a big loop system to keep entering water temp at 30 or so; while units will run below that temp, capacity falls off.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
RovicUser is Offline
New Member
New Member
Send Private Message
Posts:11

--
14 May 2010 10:59 PM
Thanks for your reply Curt. What do you think about my initial question about the spacing of the Pex Pipe, is 6" OC alright or is that oversizing things.

Rovic
RovicUser is Offline
New Member
New Member
Send Private Message
Posts:11

--
14 May 2010 11:06 PM
I am also using 300' circuits with 6 zones, 3 on each floor. Another question, when a pipe is described as 1/2" is that outside or inside and if outside what is the actual dimension. If I am buying 1/2" PEX is that osd or isd.???
Rovic
RovicUser is Offline
New Member
New Member
Send Private Message
Posts:11

--
15 May 2010 08:33 AM
Sorry, I meant " if inside what is the actual dimension "