(Before I start, please know that relationship with my installer has been tense; hence posting the questions here.)
Over the weekend, I finally got the upstairs return that the installer poorly installed connected properly. It was a job. Whew. But now, there is a return in the upstairs closet (upstairs is about 500 sq feet total, closet at top of stairs, central, with 2 huge louvered doors). When the unit is running, there is definitely a breeze going into the upstairs return. The air travels straight down a 7x14 duct, through a 5x5 hole into the basement where it turns 90 degrees, runs in a joist pan about 15 feet, then turns 90 degrees directly into the main return plenum attached to the GeoMax heat pump.
However, the unit is still going into Stage 2 cooling lockout. DATs is reading 46 degrees. Inside house temp was 73 degrees...I set the thermo to 68 to force it on to measure the return duct air flow.
I know Stage 2 cooling lockout occurs because the coil temp gets too low and unit locks out stage 2 to prevent coil freeze up.
Two questions... If the house is cooling adequately, does it matter about the lockout? I mean, wouldn't it just mean that the unit can quite happily cool the house using only stage 1. Or is it better to think that it's a problem because the thermostat is calling for stage 2 for some reason (delta not enough, etc.) and the unit is locking out?
The root question here is WHY is there a lockout...is there not enough air coming through? Is it the wrong temperature??
The air flow from the downstairs returns (much shorter path) is much more than from the upstairs. Ideally, I could pull mostly upstairs warm air into the returns, but I can't control that depending on the zone.
I measured the return ducts and this is what I found...
GeoMax unit is 4 ton - variable speed - max speed set to 1000 cfm (yeah, kinda on the low side) Air filter measures 29x32 (trying finding replacements for that size) which is 928 sq inches. There are lots of rules of thumb for a 4 ton unit, but 1000 cfm seems to require 500 sq inches of return. (formulas/rules of thumb)
The actual return plenum right by the unit is HUGE, but it's connected to 2 return ducts. One is the upstairs return detailed above (joist pan, 7x14 = 98 sq inches). The other is duct board connected to 4 downstairs return vents. The duct board measures 8x22 = 176 sq inches cross section of return duct, plus the joist pan = 276 sq inches of return duct.
The actual return duct vents are; upstairs - small - 5x5 = 25 sq inches (probably less because it has decorative metal bars on it) downstairs - four 6x12 vents = 4x72 sq inches (again, less because of the decorative metal).
In my mind, that adds up to about 313 sq inches of return, less if you approximate 0.8 for the metal on the duct vent itself....so, maybe 250 sq inches of open return duct. 276 sq inches of actual duct cross section, unit trying to blow 1000 cfm.
Am I missing something here, or does that sound really out of whack? My calculations seem to indicate my returns are HALF the size they need to be.
|