Loop Noise - knocking, thumping, tapping
Last Post 27 Jul 2013 12:39 PM by stuart.wyss. 13 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
decafdrinkerUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:420

--
09 Jul 2010 09:32 AM


System made no such noises when first installed, but progressively over the past month or two, the loops at the manifold connection have started to make weird knocking, thumping, tapping noises when the system is running. 

I'm not sure how to describe it.  It happens usually on start-up and for the first few minutes, then at occasional intervals while the system is running.  It will knock a couple of times for maybe 30 seconds, then go back to normal.

I can hear the "rushing" of the coolant in the pipes and when the knocking happens, that "rushing" changes, then goes "back to normal". 

I've contacted my HVAC guy and am waiting to hear back from him.  Just wanted to post for ideas and also in future if people have the same problem. 

I tried uploading an audio file, but it says that's not allowed.  So, instead, I posted the audio file to my website.

Please go to:   http://www.wyss-leclair.com/geothermal.wma  to hear the sounds.
heatoftheearthUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:113

--
10 Jul 2010 09:17 AM
I didn't hear the file, but sounds like you have air in your loops
decafdrinkerUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:420

--
16 Jul 2010 08:24 AM
I had actually noticed some little air bubbles inside one of the gauges on the manifold. One day I was watching, the system came on, did its usual thumping, then suddenly the bubbles were sucked out of the gauge and the noises completely stopped. Everything back to normal. I guess the bubbles went somewhere....will they return??
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
16 Jul 2010 08:59 AM
The system needs to be flushed
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
16 Jul 2010 09:16 PM
Posted By engineer on 16 Jul 2010 08:59 AM
The system needs to be flushed

and not with a garden hose hooked to the hot water heater
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
17 Jul 2010 02:05 PM
Posted By geodean on 16 Jul 2010 09:16 PM
Posted By engineer on 16 Jul 2010 08:59 AM
The system needs to be flushed

and not with a garden hose hooked to the hot water heater

The following is a loop pressure question, not a purging question.  Can the hose and water heater be used to add loop pressure if the sediment is first flushed from the water heater?  Or is it best to use a hose from an outside faucet since it is easier to just flush out the hose? 
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
17 Jul 2010 02:15 PM
Posted By geome on 17 Jul 2010 02:05 PM


  Can the hose and water heater be used to add loop pressure if the sediment is first flushed from the water heater?

sure,  we have done this when pressure was needed.
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
18 Jul 2010 11:16 AM
Thanks Dewayne. I saw our tech do this and wasn't sure if this was a good practice for adding pressure.
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
23 Jul 2010 09:20 AM
Posted By geodean on 17 Jul 2010 02:15 PM
Posted By geome on 17 Jul 2010 02:05 PM
  Can the hose and water heater be used to add loop pressure if the sediment is first flushed from the water heater?
sure,  we have done this when pressure was needed.
For what it's worth, I was at Lowe's this week.  Our store carries a 3-pack of garden hose washers with a relatively fine mesh screen built right into the washer.  This may help at least keep some larger particles from clogging the pressure ram or getting into the system since the mesh appears finer than the small opening at the tip of the pressure ram.  Less than $2.00.  I assume other stores carry these as well.
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
23 Jul 2010 09:55 AM
I would not go out of my way for these screens simply to bump pressure in system.
j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
23 Jul 2010 11:14 AM
Suggested as an ounce of prevention... :-)  For fun, I'd be happy to mail one installer one of mine to see what you think.  Just PM me.
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
Amber WrightUser is Offline
New Member
New Member
Send Private Message
Posts:1

--
02 Dec 2011 07:07 AM
Our new geothermal system has been installed for about two months now, I have noticed that the heat coming from the vents is very noisy, sounds like a blizzard is going on in the room, this is mostly occurring in the bedroom, I have not noticed it from any other rooms with the heating system? Is there a way to quiet the noise in this particular vent that is making so much noise?
AltonUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2164

--
03 Dec 2011 07:32 AM
Amber,

You might want to start a new thread so your question will not be lost.
Residential Designer &
Construction Technology Consultant -- E-mail: Alton at Auburn dot Edu Use email format with @ and period .
334 826-3979
decafdrinkerUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:420

--
27 Jul 2013 12:39 PM
Not sure if i ever posted somewhere else, but this was resolved. There was air in the system and a good purge sorted it out.