I live in NJ. I have a geothermal heat/ac unit with no conventional heat backup.
FHP model SX048-1, Pump HR003-1XXX-XXX
intermittent lockout problem, usually only occurred when large differntial between thermostat temp and house temp, only with heat
this solution typically worked: pull thermostat remove battery to clear memory, reset breaker and reinstall battery and reinstall thermostat
system takes 10-15min to reset then works, has happened a couple times this summer, there is a specific sequence to resetting thermostat and breaker and I always forget and usually just try multiple methods, i.e., reset therm first, or turn breaker off, etc.
The breaker is never actually tripped
This is not working today,
any ideas
|
|
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 26 Jul 2010 10:21 PM |
|
Is your filter clean and the condensate pan draining ok? joe |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
pansy22
 New Member
 Posts:2
 |
| 30 Sep 2010 02:23 AM |
|
I am still having problems with my compressor locking out. After my
system runs for an extended period of time, the compressor will lockout
and the auxillary will kick on. My technician has done the following
things: Replaced the CXM board twice, cut JW3 - this was not done
originally yielding a low water temp problem, installed a hard start kit
on the unit, flushed the ground loops, replaced air filters, installed a
toggle switch to disengage the desuperheater during extreme cold,
recalibrated the refrigerant pressure temperature settings, check for
high low pressure problems - there was none. What in the world is going
wrong ?
|
|
| <a href="http://superwall.com.au/">water tanks</a> |
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 30 Sep 2010 08:07 AM |
|
did he check the EWT?? |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 30 Sep 2010 08:07 AM |
|
what type of ground loop do you have? |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 30 Sep 2010 09:08 AM |
|
problem occur on heating, cooling or both...... your description makes your contractor sound incompetant. I don't know that to be true. can you write us a better description of the problem and when it seems to occur as well as loop type and what tests your contractor performed as well as no results. The trouble shooters check list might help organize your thoughts. j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|