geothermal for aquaculture operation.
Last Post 26 Sep 2010 10:26 PM by kcphuah. 19 Replies.
kcphuahUser is Offline
28 Aug 2010 01:52 PM
Hello all, my name is Ken and I am new to the forum. I am in the midst of buying a property in Lynden, WA to start up a shrimp farm aquaculture operation.  I will be using quonset greenhouse structures to house my shrimps.  First of all, the greenhouse is 150 feet long and 30 feet wide and I will be starting off with 8  - 10 of these structures first and expand the number of greenhouses as I grow.  The idea is to excavate into the ground with 2 raceways per greenhouse - and each raceway will be installed with a firestone EPDM liner and the dimension of the raceway is 130 feet long x 12 feet wide and 4.5 feet deep.  I need to keep my water temperature all year long at 82 fahrenheit and in the winter time it could get into 15 - 20 fahrenheit for the outside temperature.
This property I am wanting to purchase has no access to natural gas, and it only has access to propane.  Because of this, I have been considering installation of geothermal system to provide the heating I require for my shrimp.  I need to heat the water in the raceway and in turn the heated water will heat the ambient temperature in the greenhouse.  This contradicts to a conventional geothermal where it is tied into a heat pump and a fan to blow the exchanged air into the furnace and supply heat into homes.
1.  I love the idea of horizontal loop due to its cost and simplicity compare to the vertical loop, but with the high demand of my heating requirement, I am not sure if it will do what I need or not.  What do you think?
2.  Based on some calculation, each of the greenhouse requires 600,000 btu to keep up with the temperature I need.  If I go with closed vertical loop, how deep do you think I need to drill to have enough heat to cover all the greenhouse heating requirement?
3.  If i were to make it for on the design aspect, would it be possible to run supply and return line to each of the greenhouse.  And from each supply line I will install a coiled heat exchanger with thermostat into the raceway and a pump that is tapped off the supply line and after the heat has been exchanged it will leave from the return line.  Do you think this will work?
4.  Based on what I describe, can I get away without a heat pump?  I am just worry the solids in the raceways will clog the heat pump very soon.
I am not an engineer and I don't have any experience in geothermal heating and I am hoping you can chime in your thought of how to make this work for my heating needs.  Any ideas and thoughts are certainly welcome.  And can someone also recommend a geothermal engineer in the pacific northwest area? Thank you very much in advance and sorry for the long post.
CHuntMDUser is Offline
28 Aug 2010 02:02 PM
You might also consider solar hot water and also wood/wood pellet.  As your in the NW you need to use what is abundant and local to keep costs down.
CH
28 Aug 2010 07:19 PM
Heavy heat load. I am suspicious that it may be high.
Among solutions would be radiant loops embedded in soil outside the firestone liner.
This could have heat provided by any water heating system including solar, wood boiler, geo... the rest of the green house can also be heated by radiant or hydronic fan coils.
A professional design is in order.
Millions of BTU's can be provided by geo, but not without much upfront $$$.
Wheter it's worth it will take more calculation than you are likely to get for less than several thousand dollars.
A good ME or designer will likely save you many times your investment.
Good Luck,
Joe
29 Aug 2010 08:14 AM
I can't really picture the relationship between the raceways and the greenhouses or the purpose of them, but this strikes me as fundamentally similar to an indoor swimming pool. I too am skeptical of the 600 kBtuh load if for no other reason than that the thermal mass of such a pool is high so one likely needs only meet the average daily low temperature rather than the 5 AM temperature.
I suppose a pool teeming with shrimp needs quite a bit of oxygen mixed in or air above, so that figures into the thermodynamics
That said, the demand for such a large amount of low grade heat cries out for a thermal host such as a paper mill or power plant - facilities that endlessly reject heat into the surrounding air or water.
Finally, if I had to pick a climate suitable for maintaining large pools of water at 82F 365/24/7 it might well not be in Washington state. Momma nature keeps her shrimp in mild southern climates, but they ship easily worldwide. It may make more environmental and economical sense to move the shrimp to the climate rather than the other way around.
As Joe said, since you aren't an engineer, hire one with demonstrated expertise in the thermodynamics, hydrodynamics and psychrometrics this project certainly entails.
GeothermalmanUser is Offline
29 Aug 2010 10:31 AM
Air source heat pump pool heaters are becoming popular for heating swimming pools. That in conjunction with a propane boiler and pool heat exchanger may help reduce heating costs.
29 Aug 2010 10:47 AM
ashp pool heaters are a new inadvertant area of mine (called the rep with a question to help a friend and asked them who their local service rep was..."how 'bout you" was the reply).
Their cut out is relatively high at 45* So they are not great for winter heating in heating dominated climates.
They also aren't terrifically hearty (for year round use) but are relatively inexpensive/ton at about $500 installed.
COPs are relatively low (~ 2ish).
I'd be reluctant to recommend them for high workloads in any app.
j
29 Aug 2010 03:27 PM
600,000 BTU requirement is based on the area of the raceway and is also based at the lowest temperature during winter time.  It is always good to go a little extra then under when it comes down to the heating as the temperature of the water has a huge effect on how the animals will grow.
The reason why I have to choose PNW as a destination for such is for marketing reasons because we will be selling the products live and it is important that I can get to my immediate market in a timely fashion to command live pricing.
And in a nutshell, it is alsmost like a swimming pool that I want to heat, but coming back to the question do you all think the concept to drill vertically and tap into a heat exchanger or in floor radiant heating type set up would work?  If so, how deep do you think the drilling is requried to meet my requirements?
As for solar heting, I am worry it is not reliable because we do get a lot of glommy days in the PNW, and not sure if it will meet my needs consistently or not.  But I will look into that a little more in details.
Lastly, I am also thinking of hiring a geothermal engineer to do some pre-consultation before I makemy purchase on the property, does any one have good referrals in the PNW?  Thanks again for everyone that is chiming in.
Ken
29 Aug 2010 04:48 PM
Can you find someone who has waste heat and build next to them? Say a data center (very reliable) or a factory?
29 Aug 2010 11:21 PM
Datacenter idea may have merit, though producing 82 F in midwinter would hurt their efficiency over what is available to them in winter - maybe offer to pay for the differential COP.
Absent a thermal host, first cost for a geo system producing the required several hundred tons of heating will be very high. It is likely that the system would benefit from some value engineering, in other words, size the geo to meet only 80-95 % of the load and rely on propane for the rest.
This application is way beyond the expertise available here - while I would be fascinated to be in on such a project, I can only write in generalities about circumstances unknown to me 3000 miles away.
Down2Earth GeothermalUser is Offline
01 Sep 2010 05:04 PM
The PA Fish Commission has a large scale fish hatchery in Linesville, PA that is doing exactly what you propose. A hydrogeologist sited several high-yield 200+ gpm wells installed in areas with shallow groundwater. They use portable water to water heat pumps year round to regulate temperature in their many large indoor tanks. It is very cost effective and scalable and has been running for a good 20 years. Look at your groundwater quality, quantity, and depth. Closed loop would be cost prohibitive but open loop works great in these applications. I'll try to find more info as we were only involved due to minor heat pump repairs and some injection well scaling issues. Actually looking at your local geology you are in a broad alluvial valley close to the coast which will likely work well for high yield open loop wells (as long as salt water intrusion permitting isn't an issue). If you have access to the Nooksack river or another body of water you may be able to use that water instead of going with wells.
01 Sep 2010 09:14 PM
Down2Earth,
have you any sense of the btu load?
j
02 Sep 2010 08:29 PM
I take it that lots of light is needed for something? Not having so much glass would greatly decrease heat loss.
I thought 600K btu sounded high until I tried some numbers and got about the same. I suspect you need nat gas, passive geothermal, waste heat or a warm climate to make your business work.
06 Sep 2010 01:26 PM
Gentlemen, thank you for the thoughts & replies again.
Down2Earth, you mention the fish hatchery in PA, I tried to google it but I could not find any thing in relates to the geothermal system they have in place, do you have any info in private or links you would not mind sharing?
For my application, I think closed loop is probably the only way for me to make this happen. If it was open loop that would mean I have to discharge the water to the surface, and the volume to be discharged is quite significant and I need a really big dugout pond for it to infiltrate into the ground.... am I correct?
And 600,000 BTU is about right for each greenhouse structure and I believe with the proper insulation or heat conservation I should not require that much but then it is always to go 20% over then what I need rather than running short.
And someone mention airsource heat pump, can someone please help me understand how this may be applicable?
Thanks again for the suggestions and help. Cheers.
07 Sep 2010 10:23 PM
Posted By kcphuah on 06 Sep 2010 01:26 PM
1) If it was open loop that would mean I have to discharge the water to the surface, and the volume to be discharged is quite significant and I need a really big dugout pond for it to infiltrate into the ground.... am I correct?
2) And 600,000 BTU is about right for each greenhouse structure and I believe with the proper insulation or heat conservation I should not require that much but then it is always to go 20% over then what I need rather than running short.
3) And someone mention airsource heat pump, can someone please help me understand how this may be applicable?
1) Volume discharged around here is generally ~200Kgal/yr for heating and cooling, but there are many factors. Discharge could vary as well depending on soil etc.
2) 600K can't be "right" and 20% oversized at the same time. Geo best serves when designed to cover the bulk of the load, not load + (in heating dominated climates). Alittle bit extra to cover the odd extreme could cost considerably more than decades of auxiliary electric or propane.
The source of some debate here, many share the philosophy that geo serves best when designed to cover 92%-98% of the load, not 100+%. No one hover (to my knowledge) has ever suggested an extra 20% of capacity is appropriate.
3) There are air to water heat pumps. Used for pool or domestic hot water. I don't think they are a good fit here.
j
ReinerUser is Offline
11 Sep 2010 12:36 AM
Saw this while browsing one of the Geo manufacturer's sites.  Thought it might be a similar type of application.
http://nordicghp.com/images/stories/PDFs/Commercial-Case-Studies/aquaculture-fish-hatchery.pdf
11 Sep 2010 10:22 AM
Cool link and pdf.
82 F in the PacNW is going to be a tough load nut to crack, economically, anyway - those shrimp might be pricey.
LoobyUser is Offline
16 Sep 2010 11:33 PM
Posted By engineer on 11 Sep 2010 10:22 AM
82 F in the PacNW is going to be a tough load nut to crack, economically, anyway ....
I was thinkin' the same. Has the OP considered working with a different species of shrimp?
Stew00mUser is Offline
26 Sep 2010 11:03 AM
I am really interested in your project, I am in the development stages of a similar, yet smaller project.
We are installing 30kw of solar pv on dual axis trackers to help power the green house. Our initial plan was to grow out the prawn in tanks.
I would be interested in exchanging ideas, as we would be in two completely different markets.
give me a buzz at my emai [email protected] , I don't mind discussing ideas and I am not worry about my ideas being "stolen" as the demand of quality shrimp is so huge, and if information exchanged can help each other by gaining more knowledge and avoid pitfalls, it is a win-win for every shrimp farmers.
People Online People Online: Visitors Visitors: 199 Members Members: 0 Total Total: 199