Horizontal loops on small lot
Last Post 18 Nov 2010 07:21 AM by joe.ami. 23 Replies.
17 Nov 2010 10:30 PM
67k????what is the heat load on your house?
j
pachaiUser is Offline
17 Nov 2010 11:46 PM
Joe,
joe.ami Posted:17 Nov 2010 10:30 PM Subject: RE: Horizontal loops on small lot
j
I appreciate your interest and concern.
The report has this on the front:
Rhvac - Residential & Light Commercial HVAC Loads
Rhvac is an ACCA approved Manual J and Manual D computer program.
Calculations are performed per ACCA Manual J 8th Edition, Version 2, and ACCA Manual D.
Total Heating Required Including Ventilation Air:  45,293
Total Sensible Gain:                                29,885
Total Latent Gain:                                  2,051
Total Cooling Required Including Ventilation Air:   31,936
BTW, google gave me some information to estimate load manually,
and I came in higher than this report....but, I got the square footage right.
He is conditioning only 1/2 the house.
My spreadsheet is summarized:
                               ft^2           m^2>
Heat Load 2,043.5 189.8 76,952.5
BTU Cooling Needed
153,905.0
Tonnage Needed
6.4
The whole spreadsheet is here:   http://www.pachai.net/images/HVAC.xls
docjenserUser is Offline
18 Nov 2010 02:23 AM
Your heatloss seems to be way off for a 2000 sqf new built in New Jersey. The 45KBTU heatloss and 31 KBTU heatgain sounds about right. $67 K also sounds very high for a 4 ton system, even with 3 air handlers (why 3 air handlers?).
Unfortunately your manual J calc is more suspect than his. Much to high and generally we would expect to see cooling load lower than heating.
I like the other calc as well. How is he only conditioning 1/2 the house?
I'm also curious as to the number of air handlers.
j