5000 sq ft home geothermal 6 ton - adequate?
Last Post 16 Feb 2011 09:27 AM by opsman. 21 Replies.
Page 2 of 2 << < 12
docjenserUser is Offline
16 Feb 2011 02:33 AM
Your heatpump seems to work fine, it the generates the correct amount of heat within specs, but your KWHs do not indicate high run times. This in combination with your not reached setpoint suggests that your distribution system (ductwork, blower, dampers, zone controller etc?) is not able to deliver the heat to the house. The pump capacity seems to be fine.
www.buffalogeothermalheating.com
opsmanUser is Offline
Thank you, all, for your time and expertise. I think I am making progress -- at least I'm beginning to feel comfortable about knowing where the problem lies.
Page 2 of 2 << < 12
People Online People Online: Visitors Visitors: 98 Members Members: 0 Total Total: 98