Would desuperheater for extra heat exchanger inprove efficiency?
Last Post 09 Feb 2011 06:02 PM by jonr. 6 Replies.
tsddawsonUser is Offline
06 Feb 2011 09:20 AM
I have a 2 ton split geosystem with a desuperheater used to keep a large cotage from freezing in the winter but do not use the desuperheater since I'm not there enough to justify plumbing it into the hot water system, but I was wondering if I set the desuperheater output loop into a liquid to air exchanger would my overall efficiency be increased? The system is normally used to just keep the cottage above freezing temperatures in the winter. I think the desuperheater circuit provides an extra 6K btu's. Would it be worthwile to plumb it into another exchanger or into a thermal mass water tank in this case?  Any opinions would be appreciated.
Tim Dawson
06 Feb 2011 10:20 AM
No. The desuperheater only reroutes some of the capacity, it does not give you more.
geomeUser is Offline
06 Feb 2011 12:27 PM
I agree. Keep the DSH turned off if you are not using it.
06 Feb 2011 12:30 PM
If the DSH is unused (no water pumped through it) refrigerant discharged from the compressor carries all its heat to the air coil
09 Feb 2011 05:14 PM
Thanks for the info.
Was'nt sure if I could get another 6Kbtus out of it, but that makes sense.
Thanks again,
Tim Dawson
cnygeoUser is Offline
09 Feb 2011 05:52 PM
Actually, I think there would be a slight efficiency gain on paper - you would effectively be increasing the size of the of the condenser, which would drop your condensing temp closer to your water or air temp, reducing compressor load. In practice, though, this gain would probably be too small to measure, unless the condenser was really undersized to start with.
I second what cnygeo said.