What is the best T-stat for Geothermal?
Last Post 16 Mar 2011 09:50 AM by joe.ami. 8 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
chrisbikerUser is Offline
New Member
New Member
Send Private Message
Posts:97

--
14 Mar 2011 03:24 PM

Hi all,
I have the Honeywell Vision Pro IAQ controlling a Tranquility 27 4 ton with 5 and 10 KW backup heat packs.  The system works great and our bills are very very low through this hard winter.  We are very happy with our geo purchase.

Now that I have owned the system through the first heating season, I am questioning some of the control logic with the t-stat and wondering if there is a better moustrap out there just made for geo.

I have kept the e-heat breakers shut down and the sytem has kept up niceley.  I do supplement heat with a wood stove when it's really cold, but I think it would have been able to keep up, but I am not 100% sure.  It's definately doing better that the estimated use I got at the proposal stage.

The stat has the outdoor temp sensor, so can set e-heat lockout above a programmable set point, but if I am away the house could go cold if there is a heat pump issue.

It seems all the stats really like to keep comfort as the primary goal, and economy as a secondary afterthought.  I would like economy to be primary.

Some logic I thought a Geo Stat should have:
1) only turns on the e-heat if the inside temp drop below set point more than "x" (adjustable) degrees? (say a 2 degree drop).  ie. it can't keep up.

2) does not turn on e-heat to return from a programmed set-backs unless inside temp does not rise within "y" (adjustable) minutes?  (say 30-60 minutes with no temp rise)

3) does not turn on e-heat during manual temp adjustements unless inside temp does not rise within "z" (adjustable) minutes?  (say 30-60 minutes with no temp rise)

I would like to turn my e-heat breakers back on and would like to have a stat that would be more intelligent in it's use of expensive e-heat and not just turn it on due to set point changes.  Only turn it on as a last ditch, I am loosing the battle here, type scenario.  As you would do if you were in control of the system.

I see tons of observations of unrealized gains in economy due to stats turning on e-heat willy nilly.  I true economy based logic t-stat would really help a lot of geo folks.  IMO.

Maybe someone has found a stat that does just this and could share.  Maybe there are some models that come close? 

Any thoughts or comments are greatly appreciated.

Thanks,
Chris

heatoftheearthUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:113

--
14 Mar 2011 08:44 PM
Climatemaster's ATP32U03 will do all the things you are requesting. PM me if you need help locating one.
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
14 Mar 2011 10:18 PM
Posted By heatoftheearth on 14 Mar 2011 08:44 PM
Climatemaster's ATP32U03 will do all the things you are requesting. PM me if you need help locating one.

Any idea who makes this stat for Climate Master and what the model number would be?
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
14 Mar 2011 10:26 PM
Posted By chrisbiker on 14 Mar 2011 03:24 PM
The stat has the outdoor temp sensor, so can set e-heat lockout above a programmable
set point, but if I am away the house could go cold if there is a heat pump issue.

Easy! Put the "outdoor" temp sensor indoors. That'll allow you to
lock out e-heat unless the indoor temperature falls dangerously
low (while you're away from the house), or just too chilly (when
you're at home).

IMO, outdoor temperature information is of no use whatsoever
for controlling a water-to-air geo system, so you might as well
keep the sensor busy doing something useful.

One measurement is worth a thousand expert opinions.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
15 Mar 2011 01:17 AM
Posted By Looby on 14 Mar 2011 10:26 PM
Posted By chrisbiker on 14 Mar 2011 03:24 PM
The stat has the outdoor temp sensor, so can set e-heat lockout above a programmable
set point, but if I am away the house could go cold if there is a heat pump issue.

Easy! Put the "outdoor" temp sensor indoors. That'll allow you to
lock out e-heat unless the indoor temperature falls dangerously
low (while you're away from the house), or just too chilly (when
you're at home).

IMO, outdoor temperature information is of no use whatsoever
for controlling a water-to-air geo system, so you might as well
keep the sensor busy doing something useful.




I like the plan....
however, people insist on treating geo like a gas guzzlin furnace around here, so I put the outdoor temp sensor- outide- and set it 10F above balance point in case the sun comes out.

Most of you guys are smarter than me, and I'm probably operating contrary to the notion that "least energy" is the best concept. As an ignorant mechanic, I perceive "least call backs" and closely predicted operating costs as my "holy grail". 
If more trips and attention coulda saved my customers ten more bucks a year, I would suggest that those trips woulda cost $100 each. 
Most folks are happy when expectations are met. Most times I exceed them.
Most times I have to remind myself that my "holy grail" is not everybodies.
j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
15 Mar 2011 11:58 AM
Posted By joe.ami on 15 Mar 2011 01:17 AM
Most times I have to remind myself that my "holy grail" is not everybodies.
Yep, but In this case, the OP made it easy; he explicitly stated his holy grail:

"It seems all the stats really like to keep comfort as the primary goal, and
economy as a secondary afterthought. I would like economy to be primary."

FWIW, my holy grail is to keep SWMBO happy, and her holy grail is about the
same as the OP's -- so, I modified the controls to make a 4-stage system...

...stage1, stage2, sweater, aux,

Looby

One measurement is worth a thousand expert opinions.
chrisbikerUser is Offline
New Member
New Member
Send Private Message
Posts:97

--
15 Mar 2011 05:18 PM
Thanks for all the advise. I like looby's idea with the outdoor sensor-if I stick with the Vision Pro IAQ. It's only being used to auto cut back on indoor humidification which is not a big deal to loose that feature.

Heatoftheearth is right, the CM ATP32U03 and 04 models do what I need. Nice logic in there. I wish I found that tidbit earlier on. Hindsight is always...

I am using the outdoor venting control on my Vision Pro to control a fresh air supply, so I will loose that with the CM stat. I guess I will need to investigate some more.

As Geodean asked- are the CM ATP stats just rebranded? Anyone know which one?

@Joe- I did notice lots of folks on this site claiming these geo systems as being pigs. Maybe some due to just this issue. Our situation is the total opposite. Very low energy use is what we are experiencing. I agree with your stance on call backs and fully understand that, but if household behaviors and/or "stupid" stat logic makes the e-heat turn on what it is not "really" needed, then the whole concept of geo is shot. Almost all do geo with the promise of saving money by using less power.

Maybe manufacturers should insist certain stats and/or settings be used to really acheive the efficiencies these units can get. Bad efficiency = bad Image for geo.

At my friends house with geo, his power use was through the roof. Ended up unit was using e-heat needlessly due to setting and family behaviors. We changed a few things and now his last months bill was half (it was a bit warmer too). In my house, if I kept the settings as installed, my unit would have been using e-heat when coming up from setback and if someone did a manual temp adjust by more that a couple degrees. Total waste. IMO. I just think lots of bad stories may be due to just this and it's a shame.

If properly sized, and the unit is below balance point, e-heat is needed, but hopefully only then. All other cases are just a waste. This is the issue.

I now think our pump is a bit oversized, but I am not complaining.

Thanks again, great site. Always good to share good info. Any comments are appreciated.
heatoftheearthUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:113

--
16 Mar 2011 09:30 AM
Any idea who makes this stat for Climate Master and what the model number would be?


Sorry, no
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
16 Mar 2011 09:50 AM
Posted By Looby on 15 Mar 2011 11:58 AM

...stage1, stage2, sweater, aux,

Looby



I might have to use that line, I'll of course credit the writer.
j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!