My home is to be included as one of the featured residences in this coming Fall's Dallas / Ft. Worth Renewable Energy Tour.
For each home, a summary writeup is required for each RE technology. For me that means I have to create a summary for geothermal and solar PV.
Below is the draft I've written for geothermal. I thought I'd 'dry run' it here first. Keep in mind it's written for a wide audience, ranging from those who know little about geothermal ("I don't have a natural gas connection at my house - can I still install geothermal?") to expert HVAC installers ("What kind of borehole field heating are you experiencing from year to year?")
I live in a very hot but only mildly humid climate, so the emphasis is deliberately heavier on cooling than it is on heating. For my location, good loop design focuses on keeping the water below certain temperatures, and doesn't have to focus on how cold the water gets in the Winter.
Please feel free to make any helpful comments that come to your mind. And, you're welcome to use this for any purpose you desire - no credit required or asked for.
Geothermal Heating & Cooling System Summary
Residential Structure
Plano (Dallas), Texas 75074
Overview
Seasons: Year-round heating & cooling
Energy Type Required: Electricity (10.1 ¢/kWh) - no natural gas required
Size of Residence: 3400 square feet, single story
Average Monthly Heating/Cooling Cost: $60 (596 kWh)
Thermostats: WaterFurnace Programmable (daytime: 77° living / 81° bedrooms; night time: 81° living / 74–76° bedrooms)
Energy Monitoring: Web Energy Logger (WEL) – http://www.welserver.com/WEL0043/
System Summary
Installed: July, 2007
Technology: Geothermal-source heat pump
Number of Heat Pumps: 2 WaterFurnace Envision – 3 ton and 5 ton, both with dual-speed compressors and variable speed fan blowers
Water to Refrigerant Loop (Outside): Single loop, vertical wells, no antifreeze
Heat Pump Packaging: Self-contained (blower, compressor, heat exchanger, coil in single package – equipment is indoors; no refrigerant lines outside of package)
Location of Heat Pump Unit(s) and Air Ducts: Inside attic
Refrigerant Gas: R410A
DeSuperHeater: Available but not connected
Aux Heating Capability: Electric heat strips not installed
Number of Independent Air Distribution Zones: 4
Technical Details
(all numbers 'as built' or actuals, unless otherwise noted)
Design Temperatures: +1° F outside record low and +112° record high for Plano, TX
Cooling Capacity: 8 tons maximum; typically runs 28 - 79 KBTU/hr (2.3 – 6.6 tons); 650 KBTU/day heat rejection needed on 100°+ days
Structure Performance: 516 sf per ton of cooling capacity.
Heat Pump Performance (including blower and pumps): 21 EER (5 ton unit); 5.4 COP (3 ton), 4.8 COP (5 ton)
Inside Humidity Control Performance: 40 – 50% RH during cooling season
Lot Size: One-half acre
Water Loop: 8 bore holes (wells), each 300 ft, spaced at least 20 ft apart
Water Pipe: 1” high-density polyethylene (HDPE), approximately 1 mile in length; 60 psi static pressure
Loop Water Temperature Extremes: 61° (Winter) – 83° F (Summer)
Earth Heat Absorption/Supply: 80,000 KBTU annual heat absorption (cooling), 18 KBTU annual heat supply (heating)
Pumps: Up to 3 Grundfos UP26-116 (1/6 hp, 385 Watts each - spec)
Water Flow: 14 - 30 gpm