Please any help on dianosing a solution to a superheated aquafer
Last Post 18 Jul 2011 10:40 PM by engineer. 12 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages Informative
david rountreeUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
11 Jul 2011 10:49 PM
Can any one offer viable advice on cooling a 90 degree open loop in west florida? It serves a 57 unit condo and has dual heat exchangers with 90 plates each.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
11 Jul 2011 11:15 PM
90 is gnerally the extreme for closed loop design before seer drops dramatically. Since you are open loop, is there a reason not to try a cooling tower?
Evaporation is like ly your best friend here.
J
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
11 Jul 2011 11:44 PM
You are drawing water from one well and returning it to another?
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
12 Jul 2011 09:51 AM
Is this a Slim Jim or similar arrangement of flat plate heat exchangers sitting in a retention pond common to the condos?

If so:

1) it isn't really open loop
2) I may have an idea or two

PM me or call
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
13 Jul 2011 09:34 AM
good catch curt I focused on "open loop".

david: if it is closed loop, you may still be within design parameters. If not, get some water to evaporate, or get another heat exchanger to help heat pool.
j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
david rountreeUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
15 Jul 2011 08:29 PM
Unfortunately a tower is not in our budget at this time although we are beginning to set a budget to include a long term remedy to this problem. It is a open loop system drawing from one well supposedly 600 feet deep and returning to a diffrent site depth not known at this point. I am running 90 degree on my well side in and on my loop that goes through building which is a closed loop is consistantly running 104 and higher with ambiant temp round high 90's. I am having trouble keeping A/C's from tripping out due to compressor high temp. which alot of the units are original to building and no longer restart on their own without manually resetting breakers. my heat exchangers are alfa laval and i have two, each with 90 plates. each have 229.9 sq ft of area accordding to stamped plate on exchanger. I am having to drain from both exchangers and having to use potable water to replenish and cool closed loop side, which is becoming rather costly. Not to mention it is a balancing act. Any ideas would greatly be appreciated
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
15 Jul 2011 09:47 PM
You are pulling 90F water from 600'? Underground water flows - it's possible that a discharge well is upstream of your intake and that reversing the direction would help. The well pump is adding some heat too. Do you have an acceptable place to discharge to the surface? That at least prevents you from heating your own intake. Larger heat exchangers (or perhaps a cleaning) will bring your closed loop temperature below 100F (which might keep the systems running).
waterpirateUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:467

--
16 Jul 2011 11:47 AM
Has anyone considered bleeding off the supply like a standing colunm well to see if it has a positive effect? I am having a hard time beleiving that the well is producing 90 degree ewt. Where does the discharge water go? That would be my first priority in this puzzle.
Eric
Eric Sackett<br>www.weberwelldrilling.com<br >Visit our Geothermal Resource Center!
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
17 Jul 2011 12:26 AM
Deep groundwater in the FL panhandle should run 70 or so. I agree with the idea to temporarily bleed rather than reinject the leaving water to try to determine the cause of 90 EWT.

What is the distance between supply and reinjection wells?
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
david rountreeUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
17 Jul 2011 07:59 PM
distance between wells are around 300 feet,

Is there any uggestions on where to find flow meters and temp gauges for 6-8 inch pipe?
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
18 Jul 2011 12:57 AM
That distance should work well.

I'd be suprised if a system serving 57 condos needed much more than 4" pipe. At any rate, there are inexpensive clamp on flow meters available. Highly accurate flow meters are pricey.

Really accurate temperature measurement would require thermowells and instruments, but you could get close enough taping a thermocouple (or even a Walmart digital meat thermometer probe) to the pipe wall. I use a bit of metal duct tape for good conduction and some foam insulation to isolate the probe from ambient air.



Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
waterpirateUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:467

--
18 Jul 2011 06:40 AM
If the wells are 300' apart it should not have an issue? I would explore the possibility of some kind of re circulation? Again try to bleed off the supply, Take your ewt at the closest point to the well during the bleed off. With a system as large as yours with extensive piping a failed check valve could be allowing a certain amount of recirc in the building loop.
Eric
Eric Sackett<br>www.weberwelldrilling.com<br >Visit our Geothermal Resource Center!
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
18 Jul 2011 10:40 PM
I'd be curious to test a bleed as well.

Panhandle is a bit outside my normal AO, but I'd consider a trip to have a look
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
You are not authorized to post a reply.

Active Forums 4.1
Membership Membership: Latest New User Latest: croccohvacusa New Today New Today: 0 New Yesterday New Yesterday: 0 User Count Overall: 35027
People Online People Online: Visitors Visitors: 189 Members Members: 0 Total Total: 189
Copyright 2011 by BuildCentral, Inc.   Terms Of Use  Privacy Statement