ClimateMaster T27 - 5 ton unit (064), no aux heat. Install manual says 60 amp breaker and 6 gauge wire.
Is that correct with no aux heat?
Seems excessive to me.
Thanks in advance. |
|
|
|
|
|
|
decafdrinker
 Basic Member
 Posts:420
 |
| 18 Jul 2011 03:07 PM |
|
Just for comparison, my 4T GeoMax 2 (ClimateMaster) says 50 amp breaker and it's wired up with 8 gauge copper wire (220 VAC). The Aux Heat strips are on their own circuits, with the 10 KW stage on 6 gauge, and the extra 5 KW stage on 10 gauge. 60 amp breakers with gauge 6 sounds about right. I think my wires have a smaller ground (something like 8 gauge with 10 ga. ground) but the wire is correct. |
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 18 Jul 2011 10:50 PM |
|
Absolutely go with #6 wire. Min circuit ampacity is listed on unit nameplate as well as max overcurrent protection. Heavier guage wire helps avoid voltage dips during compressor starts - compressor briefly draws the amperage shown under "LRA" (Locked Rotor Amps) upon every start. Beefier wire combats this effect. |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 19 Jul 2011 09:26 AM |
|
min amps ~43 would permit smaller wire, but dips and long run times can really heat it up. recommended wire from CM would not prevent an inspector from passing you if you used 8 wire and 45A fuses. j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 20 Jul 2011 12:14 AM |
|
But why set the stage for needing a hard start kit a few years down the road? |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
steve_mn
 New Member
 Posts:18
 |
| 20 Jul 2011 05:32 AM |
|
Thanks everyone, will go with CM recommendation, the run is only about 10 feet.
|
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 20 Jul 2011 10:40 AM |
|
In that case 8 is probably OK. |
|
Curt Kinder <br><br>