Been lurking around on the forum here for a while, reading and trying to learn as much as i can, and i'm finally wanting to get some feedback on an estimate - if it seems on track/reasonable - for a geothermal retrofit...
Little bit o' background: House is about 17 years old in Upstate South Carolina. Existing unit is Split 3.5 ton AC unit (13 SEER single stage, not high efficiency) and NG Furnace. 2 Zones which we would do away with. Husband is committed to keeping the house 65° and currently the room at the far end of the house from the air handler gets almost no flow and that room stays a solid 10° warmer than the rest of the house. The house will not get cooler than 75 during the heat of the day, so that one room stays about 85°. Either the zone dampers are not working or the ducts are configured poorly at that end of the hosue or the unit is just undersized. Contractor believes it's probably a combination of those 3 factors. Husband also hates the NG heat that is so dry and hot feeling. So we're looking to change. Geothermal seems to make such sense but everything I read her says system design is critical, as well as an experienced contractor, so some feedback would be greatly appreciated.
The first thing the HVAC contractor told us is that systems are not designed to cool to 65°F when the ambient air temp outside is 98°F. He says 20°F is the difference all systems are engineered for, regardless of Geo, Heat Pump, Gas Furnace, whatever. That being the case (true? not true?), he's given us 2 different options for the geothermal.
Some info about the house - about 2400 sq foot ranch relatively few windows but high ceilings in approx. 1000sq feet of the space.
Here's the info from the "GeoLink" analysis. Hopefully I'm putting the right info in here.
Design Data:
Heating Load: 60k Btuh
Heating Temp Diff: 62°F
Cooling Load: 60k Btuh
Cooling Temp Diff: 25°F
Constant Fan: No
Winter Design: 22°F
Summer Design: 93°F
Internal Gains: 9,441 Btuh
Annual Load:
Heating: 55.5 million Btu
Cooling: 42.6 million Btu
Hot Water: 18.1 million Btu
HW Use: 70 Gallons/day (*for some reason assumed 4 people so this is probably at least double for the 2 people)
He is recommending that for normal people (ie people who are ok with 75° in the heat of summer) with this house, they would recommend a 4 ton system. However, due to the increased demand from husband desiring year round cave-like climate, he is recommending a 5 ton system. In either case, they would be removing the damper/zone arrangement from the attic duct work because we just don't really need it. The system would connect to a horizontal loop field, final configuration TBD, but they install, on average, 200 feet per ton of capacity. Does this sound about right? Some of the postings here seem like people have a lot more linear feet of ground loop. Does this vary based on the climate the system is installed in?
The estimates/proposals:
For the 5-ton option: Split WaterFurnace model NDZ064/NAH060 with desuperheater and horizontal loop field. Removal of existing dampers and adding adequate duct capacity to accomodate increased airflow. Installation of 2 dehumidifiers (one in basement, one in crawlspace) to mitigate mold growth potential due to unusually low indoor temperature in the house (this actually struck me as a "limit-liabilty" requirement). Total cost $27,670 (before rebates & incentives)
For the 4-ton option: Split WaterFurnace model NDZ049/NAH048 with desuperheater and horizontal loop field. Removal of existing dampers and reconfiguration of existing duct work as needed to correct airflow problem. Total cost $20,075 (before rebates & incentives)