Posted By Paul Auerbach on 03 Mar 2012 11:52 AM
To the geo professionals:
We are all seeking real world geothermal system performance data. Our company wants to meter our systems (both DX and water loops) for electrical use, pressures, temperatures, air flow. Is anyone doing this now? If so, let us know what you're measuring and how you're doing it so we may adapt the mechanisms to our systems. We all know how valuable this data will prove to be - and we will publish it. Thanks.
Paul
www.TotalGreenUS.com
I use a
Web Energy Logger to "meter" 2 WaterFurnace Envision geothermal (closed water loop) systems. Take a look at
WEL0043.
It:
> directly measures and records EWT, LWT, EAT (DB), LAT (DB), EAT %RH, refrigerant discharge line temp, refrigerant liquid line in cooling mode temp, power, run time, inside cabinet temp, and heating/cooling degree days;
> infers and records loop GPM and air CFM;
> assumes a constant Sensible/Total Cooling Ratio;
> computes and records water loop Delta T, air Delta T, Heat of Extraction / Rejection (HE/HR), Heating / Sensible Cooling Capacity (HC/SC), COP and EER.
> does not measure refrigerant or water loop pressures.
For most of the metrics, the data is 'sampled and held,' eliminating all numbers not associated with a running system.
Real time charts for some of the metrics are available at the above reference. Time period for the charts is generally one year. For all metrics, and for multiple years, data and charts are available but not online.
There's only one WEL site that I'm aware of that's measuring refrigerant line pressures. See
WEL0201. This happens to be an Earthlinked DX system. (I'm not measuring refrigerant pressures because I don't want to connect directly to the refrigerant circuits and then risk warranty challenge in case of system repair need.)
Hope this is a helpful start.