lzerarc
 Basic Member
 Posts:423
 |
| 20 Mar 2012 09:30 AM |
|
Getting ready to start a new build using geo with vertical wells. I am talking with my electrician who does many of my commercial projects, so he does great work, I can trust him, so why not have him help on my own house?
Anyway, we were talking about the service size to the house. I just assumed all along a 200a service, but he said if I was wanting geo I need to up it to 300-400a service. The proposed system is a WF, 2 ton unit and 7kw electric heat strip. Loads in the rest of the home will be hopefully lower, with ES lighting and appliances, gas range, etc.
Any thoughts/input on this? I find it hard to believe that I would need a service this large. |
|
|
|
|
|
|
Looby
 Basic Member
 Posts:401

 |
| 20 Mar 2012 10:54 AM |
|
200 amp is plenty for our 3-ton WF NDV038 with DSH
and 10 kW heat strip, on a vertical closed loop (in PA).
Everything else in the house is electric, too -- cooking,
clothes dryer, well pump, etc. No combustion, no solar.
We initially experienced a noticeable (but not otherwise
troublesome) dimming of lights at compressor start-up,
but a WF Intellistart eliminated that annoyance entirely.
BTW, the lamp dimming was primarily due to a very long
(and somewhat undersized) above-ground feed from our
rural electric service. So, it might not hurt to oversize
the service connection a little -- but the 200 amp panel
is more than adequate for our needs.
WF now offers Intellistart as a factory-installed option.
IMO, it should be standard equipment -- it would be
foolish to order a WF heat pump without one.
Looby
|
|
| One measurement is worth a thousand expert opinions. |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 20 Mar 2012 10:55 AM |
|
Sounds like 200A is fine |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
geome
 Advanced Member
 Posts:987
 |
| 20 Mar 2012 12:32 PM |
|
Posted By Looby on 20 Mar 2012 10:54 AM
WF now offers Intellistart as a factory-installed option.
IMO, it should be standard equipment -- it would be
foolish to order a WF heat pump without one.
+1. Extremely useful for a standby generator too. Factory installed IntelliStart should be reasonably priced, and should be eligible for the 30% tax credit (since the price is rolled into the unit cost.) Same story on our lights dimming pre and post IntelliStart. 200 amp service here too. We have 5 tons split between two units. Electric water heater, but propane dryer and range. |
|
| Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon. |
|
|
SkyHeating
 Basic Member
 Posts:203

 |
| 23 Mar 2012 11:19 AM |
|
You sure you trust your electrician for your own house? It sounds like he is either way off or just doesn't have a freaking clue. 7KW should be about 45 amps I think, normally every 5KW is 30 amps, plus a two ton unit is only 20-30 amps at most. And as others have said, intellistart should be included with every unit, we don't sell a unit without it. |
|
Visit my Youtube channel for product reviews and customer testimonials http://www.youtube.com/user/skyheating1 http://www.welserver.com/WEL0626/
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 23 Mar 2012 12:29 PM |
|
One of our utilities has begun requiring soft start. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
jonr
 Senior Member
 Posts:5341
 |
| 23 Mar 2012 03:11 PM |
|
Since I've heard that inverter based mini-splits are the solution to everything (that's a joke), has anyone measured to see if they do a slow start that would make them work with small generators?
|
|
|
|
|
SkyHeating
 Basic Member
 Posts:203

 |
| 27 Mar 2012 12:56 AM |
|
Posted By jonr on 23 Mar 2012 03:11 PM
Since I've heard that inverter based mini-splits are the solution to everything (that's a joke), has anyone measured to see if they do a slow start that would make them work with small generators?
I have never measured but everything i have seen from the manufacturer shows that they soft start because in Japan and high density areas where these are prevalent they require it. |
|
Visit my Youtube channel for product reviews and customer testimonials http://www.youtube.com/user/skyheating1 http://www.welserver.com/WEL0626/
|
|
|
GTJON
 Basic Member
 Posts:112
 |
| 17 Apr 2012 02:11 PM |
|
Hi and thanks for the EDU ! @ 10 kw , although using 60a breakers for heat and sometimes #4 thhn for carry through unheated spaces; I have found 43-46 amps on 240-250 volts; -and 22-23 a on 5kw strips. old 100a services have had no problem (exchanging to better panels with job) with 35 a RLA and smaller with even 10KW strips (5, wired separately-contacted, for emergency use ) - also b/c of the Dual Compressor 3-Staging, in a smallest 17MBTUh and 23MBTTUh combo "rated's size 4.0 " sometimes, it acts as a pretty soft start, and no-problem starts with 12 hp generator in one case only seen. 200a , depending on all else totaling: actual running combined under 80% at under 160 amps, has worked with 2) 4-size, and 15 kw strips (KW alone 66-68amps), clean-cool-pasted breaker contacts throughout panel setup and sub panel(s). |
|
|
|
|
GTJON
 Basic Member
 Posts:112
 |
| 17 Apr 2012 02:33 PM |
|
BRISTOL's V- is adjustable to 5-staging set or other.
|
|
|
|
|