Q's:
1) Can these units be used on our system which has NO antifreeze in the condenser water?
2) Or will we be at risk from the reheat coil freezing and rupturing?
3) And if we cannot use them on our system with NO antifreeze, is there a way to disable Climadry so we won’t use it and it is not at risk of rupturing?
4) Maybe somehow empty the reheat coil of water and then remove power from the three way valve and Climadry pump and simply not hook up a dehumidistat?
His q's are as I may understand:
1) Workable without antifreeze ?
YES - IF about using controlled minimum temperature of leaving water which is in all cases in a public posting- to be found at above 38F/LvWtr at 3-to- 3.3 gpm per ton of compressors[cT] (read label inside these units for real tonnage). Some OEM techs at 2 gpm/cT LW allow "above 39F".
2) see 1)
3) YES. and CM techs will help you find the wiring to controls that can be disabled. and 4) See 3).
call Joe (his advertised website is in his post) he really is very patient and considerate and may be of further help and tells you when he does not know something