I'd get some more data before you go to a major expense.
Here's some data for residence in a hot Dallas climate (79 100°+ days last year) . This may help to frame how big the problem may or may not be. Structure is a 3400 sf, single story residence. With it being single story, attic expanse is significant.
Insulation is blown-in fiberglass, at R-38 amount. Nothing else special about the attic - under eave vents and three wind powered exhaust fans in the roof.
Here's a chart showing the
hourly avg attic temp for almost 4 years (measured outside of the cabinet of 1 of 2 geo units). Key things to note are: (1) peak temp is about 135° F, (2) for only a few days each summer is the peak above 130°, and (3) it's about a one and a half month period where peaks are constantly above 125°. I'm getting these conclusions from the 2009 data section of the chart because in Jan. of 2010 I installed a lot of solar panels on the South facing roof and indeed you can see about a 10° reduction in the summer peak temps.
OK, that's the extreme. Here's another chart showing the
daily avg attic temp. Key things to note are: (1) the highest avg daily temp stays at or below 104°, and (2) for only a few days each summer is the avg daily temp higher than 100°. In fact, it's about a one month period where avg daily attic temp is above 95°.
And here's the broad look. Here's another chart showing the
monthly avg attic temp. Key things to note are: (1) Only one year does the avg monthly temp approach 100° (2011, the year we had the record heat wave); and (2) otherwise the avg monthly attic temps stays at about 95° or lower. (Parenthetically, note that the solar panels affect much more instantaneous peak temps, and not monthly avg temps.)
So the above is the environment to consider. Your actual temps will be a little higher with a shorter roof height, and a little lower with a higher roof height. I don't know how the attic floor area sf affects the numbers - the attic floor illustrated here is 3400 sf.
Now let's look at what's happening inside the cabinet where the compressor and electrical parts are located.
Here's a chart showing the
hourly avg inside cabinet temps. Key things to note are: (1) peak temp is about 120°, 15° less than the ambient peak; (2) for only a few days each summer is the peak above 115°, and (3) it's about a one and a half month period where peaks are consistently above 105°. In this case I'm able to use the entire chart as the solar panels are not showing any affect on the inside cabinet temps.
Now let's look at the
daily avg inside cabinet temps. Key things to note are: (1) the highest avg daily temps over 100° are limited to a few days each season (and for 2 of the 4 summers shown the avg daily temp never got to 100°); and (2) it looks like there's about a month's worth of days where the avg daily temp inside the cabinet is above 95°.
And here's the broad look for inside the cabinet temps. Here's a chart showing the
monthly avg inside cabinet temps. Key things to note are: (1) the highest montly avg temp ranges from 94 to 98° on a season by season basis; and (2) inside the cabinets are generally at or below 94° every summer on a monthly avg except for occasional years where you may get a couple of months 1 or 2° higher.
I don't know or remember where you're located. In case you want to interpret what you may expect at your location, here's a chart that show the
hourly avg attic to outside temp difference. Here you can see the peak difference is about 35° for a couple of days in the 2009 summer. And that it's about a 30° peak difference for about 4 weeks of hot days. (The effect of solar panel installation is most pronounced on this chart).
Lastly, on this
summary page, if you scroll down just one page, you can get an idea of the roof slope to compare to what yours may be.
Conclusion?
Based on the data that I've got, if I were you, I would do 4 things:
(1) Proceed with putting the unit in the attic;
(2) Carefully make sure all duct work is well sealed, particularly on the return side;
(3) Put R8 wrap on steel duct and/or use R8 flex duct (
see example here).
(4) Not proceed with the major expense of building a closet around your unit in the attic, or the major expense of foaming the underside of the roof.
Short summary? Get on with putting in the unit in the attic, make sure all good installation procedures are followed, and don't bother with the expense of a closet or foam.
Hope this all helps.
Best regards,
Bill