Piping multiple DSH diagram - your input please!
Last Post 07 Jan 2013 08:28 PM by DJV. 3 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
DJVUser is Offline
New Member
New Member
Send Private Message
Posts:80

--
07 Jan 2013 10:02 AM
I have attached a portion of my flow diagram I am working on for my home.

I have a packaged and split system in the basement that both have DSH options - They will feed a 50 gal storage tank and them progress to my water heater ( AO Smith HYB-90N Hybrid )

I have put check valves on the DSH Supply lines and wanted to see if there was anything else I was missing  - the remainder of the valvinf is per the climatemaster diagram.

Thanks in advance
Dave

DJVUser is Offline
New Member
New Member
Send Private Message
Posts:80

--
07 Jan 2013 01:09 PM
I also plan on using 1/2" copper to the tank - would both supply and return lines be hot without the pump running?
ACES-EnergyUser is Offline
New Member
New Member
Send Private Message
Posts:67

--
07 Jan 2013 06:49 PM
Make sure your check valves are rated for the correct temperature. Most check valves at supply houses are only rated for 100F. Just ask for a heating check valve.
www.ACES-Energy.com
DJVUser is Offline
New Member
New Member
Send Private Message
Posts:80

--
07 Jan 2013 08:28 PM
great tip - thanks!