I'm finally getting close to pulling the trigger on Geo after about a year of thinking about it. For those interested in my struggles, see these threads:
http://www.greenbuildingtalk.com/Forums/tabid/53/aff/13/aft/80100/afv/topic/Default.aspx
http://www.greenbuildingtalk.com/Forums/tabid/53/aff/13/aft/80332/afv/topic/Default.aspx
http://www.greenbuildingtalk.com/Forums/tabid/53/aff/13/aft/80857/afv/topic/Default.aspx
For those who would like the short story - I have a 2100 sqft ranch in Essex MA. I've lived in it for one year. I'm currently heating with electric baseboards and a wood stove insert I bought used after seeing my first heating bill. I have a full and open basement. I recently upgraded my insulation to R55/60 in my attic and did air sealing with a blower door test showing about 2.5 ACH/50. All windows are casement double pane, and although I haven't, I plan to insulate my foundation walls (I found in the winter they were in the mid 40s and in my mind is my last major source of heat loss). Every contractor I had quote me told me to plan on 4 or 5ton for geo to work right. So I suffered through the winter to see what my actual load was. I've taken out 600KWH per month for my baseline usage. Below is that info:
As you can see, in general you can see what the insulation did for my heat load. You can also see what the wood stove did. Finally, you can see that This winter my load never exceeded 30K. The house temp was generally 60-68, more often than not probably 62-65 which wasn't particularly comfortable. My wife was on maternity for a portion of the heating season and thus heated all day. After she went back to work, we turned the heat down during the day. Based on this info I'm confident my heat load should be 3 tons. Thoughts?
The contractor that I've selected is proposing the following:
Equipment and Services:
1. Supply and install 3 ton Bosch Geothermal 2 stage package unit with EMC motor.
This equipment qualifies for 30% federal tax credit (please see your financial advisor) and Utility rebates.
2. One Desuperheater.
3. One 9.62 stage electric back up heater.
4. Geocomfort 2 pump flow center with hose kit.
5. Complete duct system with registers and grills.
6. One programmable thermostat.
7. Anti-freeze the system.
8. All ductwork to be sealed and insulated.
9. Mechanical permit.
10. Test operate.
The well proposal is as follows:
(1) 510’ Bore hole
Loop Length: 510’
Diameter of pipe: 1 ¼ ”
SCOPE OF WORK
Up to 40’ of 6” pipe casing into bore hole
Drilling of vertical bore hole*
Install vertical ground loop
Grout vertical bore hole*
Install horizontal lines
Pressure test system
Purge and fill system up to the flow center with 20% glycol solution
Trenching and backfilling of horizontal lines
How does this look to everyone?
I realize that in order for the desuperheater to be useful, I will need a buffer tank. Does that tank need to be the same size as the water heater?