Climatemaster T27 - HP fault, code 2
Last Post 25 Feb 2014 09:28 AM by joe.ami. 1 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages Not Resolved
steve_mnUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
24 Feb 2014 12:02 PM
Hello, We have a technician looking at it now, furnace is 160 miles North (Northern MN). Symptom is intermittent, for instance, yesterday while we were working on the house(new construction)it ran fine for several hours and then would barely run when we left, drained water, heaters in strategic places etc. When it runs, it runs well, this started 2 weeks ago. Hasn't gotten worse or better as far as I can tell. Ohmed the HP sensor and it was 0. Should have ohmed at pins 1 and 2 at CXM connector but didn't. Once when it was about to start yesterday the compressor made a clunk and locked out, it later started ok. Just want to keep the tech honest, he got me very worried about the compressor, some reed valve, where blades can break off etc...... Any comments would be appreciated. Thanks Steve
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
25 Feb 2014 09:28 AM
One, Climatemaster does not want it's equipment used for construction heat.

Why is it locking out?

FP2 can be a thermistor, a pressure switch, inadequate GPM, low entering air temperature, low refrigerant charge........
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com