Hydron Heating Issue
Last Post 10 Oct 2015 10:20 AM by geodean. 2 Replies.
RebokIIUser is Offline
05 Oct 2015 04:32 PM
Hello. New to the forum. Have been here to read before, but now have an issue, so i signed up. I have an 8 year old 2.5 ton Hydron unit. Has worked well to this point. I just put it into heat mode this weekend and am not getting any heat. I have checked the pump pack and water is definitely flowing. The compressor comes on, and the unit appears to run fine, however, there is no difference between the EWT and LWT. Typical temp difference in years past has been +/- 9 degrees F. No codes are being shown. Wondering if there any ideas what it could be. Thanks.
chrsUser is Offline
05 Oct 2015 09:45 PM
When you say no heat out, is it blowing air, but the air is uheated? Or is there no airflow? If it was a refrigerant leak, it should trip out on low pressure. Maybe it's a problem with the reversing valve, which could be stuck in a way that it's not effectively heating or cooling? A couple of things you could try would be running in cooling mode again to see if that works, and switching modes back and forth a few times to hope to get it unstuck if it's stuck. If it works in cooling that's a pretty big clue that it's the reversing valve. You can also feel the tubing at various places inside and if you know what's what, learn something from what is getting hot or cold (or not) being careful to avoid anything electrical.
Do you have a desuperheater, and is that doing anything?
And do you have backup heat?
maybe the fan is running but the compressor.
People Online People Online: Visitors Visitors: 523 Members Members: 0 Total Total: 523
