Geothermal 4" well need assistance
Last Post 01 May 2016 11:12 AM by jonr. 3 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
islandsurferboyUser is Offline
New Member
New Member
Send Private Message
Posts:2

--
30 Apr 2016 04:03 PM
I have a 4" well with a pump that get me 4 gpm. I'm adding a 4 ton geo heat pump system and need to pull the old pump out and put in a new one, thinking I need at lease 10-12 gpm to runt it and the house The well hits water a 40 feet but the well is 200 ft deep. What is the best energy efficient pump to use
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
30 Apr 2016 05:50 PM
You might want to check the wells yield before going too far. Ie, you are sure can it continually produce > 10 gpm?

Variable speed pumps are attractive. Always carefully check the flow and pressure curves (based on worse case level, not the total depth).
islandsurferboyUser is Offline
New Member
New Member
Send Private Message
Posts:2

--
01 May 2016 09:07 AM
Thank you Sir - I will have my well guy check. If all is good - any suggestions on a pump?
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
01 May 2016 11:12 AM
You need the water level first. Ie, worse case (12 gpm + other usage (much much?), low water table), how deep is the water?

In the mean time, read this:

http://www.greenbuildingtalk.com/Forums/tabid/53/aff/13/aft/83335/afv/topic/Default.aspx