Climatemaster tranquility "Service Needed" message
Last Post 14 Aug 2018 01:39 AM by alexschmidt99. 5 Replies.
alexschmidt99User is Offline
12 Aug 2018 01:56 AM
Hello - I have a Climatemaster tranquility heat pump with the iGate communicating thermostat. I have not had any problems with the unit since it was installed in 2014 and it has performed perfectly. Near the start of this heating season the thermostat displayed a "service needed" message. Operation of the heat pump did not appear to be impacted.
I checked the troubleshooting guide and it appears that what is triggering this "service needed" message is that the refrigerant temperature is getting higher than ideal. Th troubleshooting guide states that this condition indicates the heat pump isn't operating at peak efficiency. It states that the areas to check are poor water flow or poor air flow.
I have checked the basic items - there do not appear to be any air blockages and I replaced the filter. My loop remains pressurized, however I annually have to bump up the pressure. It falls to about 15 PSI over the course of the year and I pump it back up to about 50 PSI using a valve I installed in the manifold. I flush water through the re-pressuring system I have in order to get any air out of the re-pressurizing valve and hoses before opening the loop so I feel fairly confident that I am not introducing air into the loop.
As of now I think my problem is in one of three items. Either my blower fan is not moving as much air as it should through an issue with the blower, my pump is not moving as much water as it should through an issue with the pump, or I have air in my loops that is preventing the pump from operating as efficiently as it should.
My communicating thermostat reports on the blower RPMs and "Target CFM". The "Target CFM" is as it should be for stage 1 and stage 2 operation, however I think this is only a target and not the actual airflow. I am not able to locate a chart correlating RPM to CFM. Does anyone know of a chart or a way to measure the actual airflow?
My thermostat also reports my pump speed. Oddly, whenever I check the pump speed is always at 15%. I do not have any sort of override set, so the heat pump logic controller is determining 15% speed is the ideal speed. Does anyone know of a way to verify the water pump is functioning correctly? I can enter into manual operation and run the pump at speeds higher than 15%, but I don't have any way to verify that the pump is actually pumping water at a higher speed.
Last, can anyone describe the sound of air cavitation in the pump? I've been told the sound is obvious, but I don't hear anything unusual from the unit when it is running.
Any other thoughts or suggestions are much appreciated.
Where you live: Kent County, Delaware
2) Heat loss/gain calculations for your home: I can try to dig these up if anyone thinks it is relevant.
3) Brand, size (model), age and type of heat pump: Climatemaster Tranquility 22 Digital (TZ), 3.0 tons, 2014 vintage, with communicating thermostat.
4) Type of loop field (open/closed/vertical/horizontal) size and design parameters: closed horizontal raceway with 3 loops at 600' length each. 3/4" HDPE.
5) Average cost/Kwh of electricity and consumption: I can gather this info if anyone thinks it is relevant.
6) Entering and leaving air temperatures (EAT, LAT) measured immediately upstream and downstream of the heatpump: 71 deg/52 deg
7) Entering and leaving water temperatures (EWT, LWT) measured at the geo system: 79.3 deg/123.9 deg
8) Percent of load to be covered by geo and balance point: 100%, electrical resistance heater included in geo unit supplements geo when temperatures drop below ~25 degrees.
9) Installer's assessment of your systems operation. Self install. 10) Projected operating costs, actual operating cost and previous heating and cooling costs: I can try to dig this up if anyone thinks it is relevant.
arkie6User is Offline
12 Aug 2018 05:05 AM
You reported: 7) Entering and leaving water temperatures (EWT, LWT) measured at the geo system: 79.3 deg/123.9 deg
I assume this is cooling mode? That high differential temperature indicates insufficient water flow. I assume your unit has the Vflow option with internal variable speed loop pump. There is a way to adjust the pump flow characteristics using the iGate thermostat. You can set the pump to control based on differential temperature (most common and efficient method of control) or at a fixed speed and 15%-90% is a valid range. It sounds like your pump control may have reverted to fixed speed at minimum. Have you had any power outages or surges that may have caused this?
If you don't have the installation manual for your communicating thermostat, you can download here: http://www.climatemaster.com/geothermal-dealer/tz/
The manual walks you through the steps to configure your variable speed internal pump control with examples given such as: PUMP CONTROL = DELTA T (or FIXED), HEATING DELTA T = 7 F, COOLING DELTA T = 10 F, etc. Make sure your PUMP CONTROL is set to DELTA T. If your pump control shows Delta T and a reasonable value of around 10 F in cooling, then there may be a problem with your unit control board outputting only the minimum setting to the pump regardless of the setting.
Does your unit have the DXM2 control board? If so, what does the Fault and Status LEDs indicate?
12 Aug 2018 02:57 PM
Yes, this is in cooling mode.
Using the directions in the user manual I checked the pump settings and it is set to delta T with a cooling temperature differential of 10 deg. I also checked the fault history and there are several high pressure faults listed, although I am not sure how old they are.
As a test, I changed the pump setting to fixed speed and kept the default speed of 90%. After about 15 minutes of cooling operation the LWT and EWT are 86.0 and 81.8. I also cleared the fault history when I changed the pump setting to fixed speed and after 15 minutes the high pressure fault had not returned.
I have now switched the pump back to delta T operation. I will check later today to see if the faults return.
The only fault listed after 24 hours is a "Low Performance" fault
duplicate post
duplicate post
Membership Membership: Latest New User Latest: croccohvacusa New Today New Today: 1 New Yesterday New Yesterday: 0 User Count Overall: 35027