bstump
New Member
Posts:13
28 Mar 2022 12:11 AM
My HVAC tech says we have to run an 11" x 26" trunk line the whole length (or most) of the house. I paid extra money to have 24" deep floor trusses (needed to span the entire basement without support beams), but the webbing does not allow 11" x 26", only 11" x 18".
I have posted a link below and have a question. I used a couple calculators online to figure out effective duct lengths, and I don't think there's a single duct that needs to push more than 100 CFM (10' ceilings) for more than 75 feet.
Is there a way to have the main trunk (green in pic) ONLY be run in the 24' 8" section and then run supply only ducts (blue in pic) from there? I think I'm going to talk to Energy Wise this week to see, but I don't want to get my hopes up. I'm quite frustrated that this has happened because I specifically paid more for the floor trusses to be able to not have to hang ductwork from my basement ceilings...
This picture isn't the duct "plan", it's just for an example for my question.
https://drive.google.com/file/d/1x8fYD87aJLMCI2z4wbsZWp1zN7P2YHvy/view?usp=sharing
newbostonconst
Advanced Member
Posts:736
29 Mar 2022 01:48 PM
I don't see why you can't make individual runs to each register. I did this and it is just a lot of ducts/flex to run. I am sure it will add a lot of cost.
Might want to try a HVAC forum....
"Never argue with an idiot. They will only bring you down to their level and beat you with experience." George Carlins
smartwall
Veteran Member
Posts:1197
29 Mar 2022 02:28 PM
Energy Wise is the best place for a solution. I've been recomending them for 15 years
sailawayrb
Veteran Member
Posts:2273
29 Mar 2022 02:45 PM
+1 for Energy Wise.
11" x 26" seems like a very big duct. I would want to know what is driving that requirement? What about doing small duct high velocity HVAC?
This saga does illustrate why doing an integrated building design/build is important. All to often HVAC is accomplished as an afterthought which can lead to these sort of issues.
Borst Engineering & Construction LLC - Competence, Integrity and Professionalism are integral to all that we do!
You are not authorized to post a reply.
Green Building Forums
--General Forum - Residential
--General Forum - Commercial
--Green/Energy-Efficient Design and Planning
--Green/Energy-Efficient Building and Construction
Green Building Technologies
--Insulating Concrete Forms (ICFs)
--Structural Insulated Panels (SIPs)
--Radiant Heating
--Geothermal Heat Pumps
--Solar and Wind Power
--Windows/Doors and Interior/Exterior Finish
--Appliances, Lighting and Kitchen/Bath Fixtures
Feedback/Support
--Rules, Instructions and Announcements
--Suggestions/Feedback
--Testing Area
Forums
>
Green Building Technologies
>
Geothermal Heat Pumps
Active Forums 4.1
Membership:
Latest:
HotnCold
New Today:
0
New Yesterday:
0
Overall:
34723
People Online:
Visitors:
126
Members:
0
Total:
126